why DG,Transformer,UPS capacity will be tell in KVA but not
in KW?
Answers were Sorted based on User's Feedback
Answer / sujith
The active power in KW is= VICos(angle B/w V&I).
The angle is dependent on the load connected and hence the
active power varies. So KVA only can be mentioned for the
above mentioned supply sources.
| Is This Answer Correct ? | 12 Yes | 3 No |
Copper loss depending upon the voltage .core loss depeon
the current. both the lossse are meassure in voltage and
current thats why we are mensione in KVA .
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / srikanth
In DG the power factor is always unity that means cos=1
so the value of power is P=VI
P=VI IS FORMULA FOR KVA
SO DG IS IN KVA BUT NOT IN KW
| Is This Answer Correct ? | 3 Yes | 5 No |
Answer / puneet kapil
First of all get clerar with the term KVA and KW
KW is the real power or active power
that means the amount of power that is available to do real work.
And KVA is the apparent power,that means
only a part ogf apparent power is available to do real work
rest or remainder is simply the excess current.
Now the question arises why to mention KVA the apparent power,
if only we can use a part of it...
Answer..... the rating of electrical appliances is dependent om the amount of current they can sustain,but KW does not give the actual amount of current that electrical equipment
can carry which is given by KVA...
I hope its clear now :)
| Is This Answer Correct ? | 0 Yes | 4 No |
WHAT IS ND RELAY AND HOW DOES IT WORK?
why the amount of voltage generated at power generating stations is 11 KV only....?
what is the formula to convert from KVAr to current?
1 Answers Halcrow International Partnership,
why can not run two different phase circuit in to the same conduite
what will happen if the input of a transformer is dc?
Is necessary Protection CT, CLASS - 5P10 fitted at Incomer side of main Breaker ? Why ?
How does the sensitive earth fault protection provided by cbct for motor can help in reducing the size of cable used to supply the motor?
why generator one end side star neutral point given? if this point not given what happen?
A 100W electric lamp is supplied from a 115V, 60HZ source. The peak instantaneous power dissipated in the lamp filament is
A 1F capacitor is charged to 100V initially. A 1H inductor is connected accros the capacitor througha a switch. The current in the circiut when the switch is closed is____
what is inrush curent.
Why DC Currents are not used in transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)