Explain the Term in CT Name Plate – Class: 5P10
Answers were Sorted based on User's Feedback
Answer / chr
5P10 DETERMINES 5% ERROR IN MEASURING DATA FOR 10 TIMES THE
CURRENT FLOW IN THE CT.
Is This Answer Correct ? | 37 Yes | 3 No |
Answer / r. r. patange
In 5P10, P stands for protection, there are two main
classification of current transformer
1) Metering CT
2) Protection CT
so above mention CT can be use for protection purpose.
the first digit (5) stands composite error.
composite error - it nothing but the differance between
instanteneous RMS valuve of primary current and secondory
current, multiply by transformer ratio.
the last digit (10) is stand for the times of primary
current. It means this protection CT can capable of
measuring current of 10 times than its rated during fault
condition with error of 5% and without getting saturated.
Is This Answer Correct ? | 31 Yes | 3 No |
Answer / barkha thakur
P indicates the protection level & 5 indicates the accuracy
it means when sec current is increased by 10 times, ct
senses the current with 5 % error
Is This Answer Correct ? | 32 Yes | 5 No |
Answer / sangram
first i explain the term:- 5 is a class of accuracy, p you
should use for protection purpose, 10 you should load up to
10VA.
you should use this CT for protection purpose, and the
burden rating should 10volt Amp at 100% load pass in
primary, you should allow +/-5% error for this CT.
Is This Answer Correct ? | 14 Yes | 7 No |
Answer / wasim maniyar
For example, CT is specified as 15VA, 5P10 where 15VA denotes burden, 5 denotes composite error and 10 denotes ALF(Accuracy Limit Factor).
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / faheem
according to my study the there are two type of accuracy
class 5p & 10p 5p=+-1 % error,and 10p=+-3% error.and last 10
shows the accuracy limit factor 5,10,15,20 and 30.. It means
this protection CT can capable of
measuring current of 10 times more than its rated during fault
condition with error of +-1% and without getting saturated.
Is This Answer Correct ? | 0 Yes | 7 No |
which are the criterias needed to select the kind of neutral earthing(solid earthing,resistance earthing,etc.) at various voltage levels in electrical distribution?
why Square root 3 used for three phase?
function of soft starter .
why does a dc machine has high efficiency while working as a generator than as a motor
how will we calculate the copper wire load..
how the capacitor work on dc?
How do you select a cable size(cu&Al)for a particular load?
how on load transformer is chnage the Tapping ?
why transformer cannot rotate though the princplebehind induction motor is similar to a transformer?
how can we change the supply voltage?
Define what is the function of anti-pumping in circuit breaker?
I have suguna 3 hp pump for my agreeculture work.It deliver the water from 45 feet well .I suffered by powercut.During powercut i got 2phase supply only .My question is can i run the pump in 2 phase supply using capacitor?.Can u explain me how to connect the capacitors?