How can we calculate the cable size???
plz give the formula !!!!!
Answers were Sorted based on User's Feedback
Answer / prashant
The basic equation is
P = 1.732VIcosA, where CosA can be taken as 0.85
V = 415 V
P = load
From this u have to find the current I and then using the
table select a suitable cable and cable size which can
withstant the current.
Is This Answer Correct ? | 16 Yes | 6 No |
r=v/i and r=&l/a where &=specific resistance of conductor,
now v/i=&l/a then i=va/&l
i=current.v=voltage ,a=area of conductor. &=specific
resistance of condutor ,l=length of condutor
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / bob
first you should know permitted voltage drop U0% then calculate the cable size
A= 1.73 × I × l× P.F / 56 × U × U0% mm2 ( 3 phase load )
I: load current
L:distance
p.f: power factor
56: specific conductivity of CU and 34 for AL
then compare the result with table to make sure voltage drop and current withstand is Ok
make enough reservation for load current by multiply the load current by 1.25
Is This Answer Correct ? | 3 Yes | 1 No |
how will be power factor while using the resistive load and Capacitive load?
what are the differance between neutral and earthing?
what is the working principle of ceiling fan and table fan?
10 Answers ABC, Tata Steel Limited,
Is it really necessary to have reactive power in transmission line to transfer the power from one place to other?
How equivalent impedance is calculated in thevenin theorem?
What is open delta Xformer? It's adavntages & Use?
In how we connect watt meter for open & short circuit test of a single phase transformer.
In 11kv transmission line whats the maximum power can be drawn?
two parallel conductors are carrying the current in the same direction.which of the following statements is true? (a)there is arepelling force between the conductors (b)the force increases when the distance between the conductors is increased (c)there is an attaracting force between the conductors (d)the force increases when the distance between the conductors is decreased
Can we pass 11kv power in 1.1kV voltage grade cable.If not why?.
can we keep open the secondary of current transformer?
Which thing is maximum in RLC circuit at resonance a)power consumption b)inductive current c)capacitive voltage