Why OLTC(On Load Tap Changing)transformer is not recomended
for improving voltage instability?
Answers were Sorted based on User's Feedback
Answer / iamdon
Voltage instability is due to following reasons:
1)Gradual increse in load.
2)Loss of generating unit or heavily loaded line
3)Poor cordination amoung control action to avert the
situation etc.
In all the cases the system is insufficient to cater the
reactive power requirement of the load.It leads to the
reduction in voltage at load end.
OLTC transformer increases the voltage level at load side
so Q requirement of load increases.The system is already
running short of Q, so it is not possible to supply this
incresed Q by system.This leads to more voltage dip at
load.In this way, instead of stabilizing the voltage, OLTC
transformer aggerevate the voltage instability.
Author:arbelectbit@yahoo.com
Is This Answer Correct ? | 5 Yes | 0 No |
oltc worked in step not in pid mode only avr worked in pid mode
Is This Answer Correct ? | 2 Yes | 1 No |
how to measure winding resistance of single phase motor?
What is the Surge for 1.1 Phase Induction Motor(For Eg.1Hp) 2.3 Phase Induction Motor(For Eg.1Hp) 3.AirConditioner(For Eg 1Ton) 4.Refrigerator(For Eg 180Ltr or 160kW) 5.Induction Cooker 4. Ceiling Fan
What do you mean by reverse current braking of an induction motor?
The unit of resistivity is:(a) ohms(b) ohm millimetre(c) ohm metre(d) ohm/metre
in HT service 3ph 4 wire service Y-phase voltage shows zero . whether it is meter fault? or what be the reason ? if y-ph voltage zero ,can current is recorded? reasons for failure?
What is FTA card? How it works?
How the neutral earthing is connected in DG alternator
What will be the resultant out put voltage when two different voltage rating batteries are vconnected in parallel? pls. answer with example if available.
How to measure size of cable on a given load
0 Answers Green India Engineering Solutions,
Why we does earthing for transformer neutral point
How to do the REF Stability test for power transformers in Site?
How to calculate 5hp 415v 3phase 2800rpm Ac motor full load current with out tourgh