Why OLTC(On Load Tap Changing)transformer is not recomended
for improving voltage instability?
Answer Posted / iamdon
Voltage instability is due to following reasons:
1)Gradual increse in load.
2)Loss of generating unit or heavily loaded line
3)Poor cordination amoung control action to avert the
situation etc.
In all the cases the system is insufficient to cater the
reactive power requirement of the load.It leads to the
reduction in voltage at load end.
OLTC transformer increases the voltage level at load side
so Q requirement of load increases.The system is already
running short of Q, so it is not possible to supply this
incresed Q by system.This leads to more voltage dip at
load.In this way, instead of stabilizing the voltage, OLTC
transformer aggerevate the voltage instability.
Author:arbelectbit@yahoo.com
Is This Answer Correct ? | 5 Yes | 0 No |
Post New Answer View All Answers
Explain the different regions in frequency response?
in ACB breaker requireding 3200Amps. buscoupler getting OFF mode and again it reset and getting normal position give me a required answer?
Define filter?
why lightning arrestor are made in two stack of insulator but why not cvt
The moisture in air will condense at
WHAT IS DEGREE OF COMPOUNDING IN D.C MACHINE MEANS? HOW TO READ THE OPERATING CHART FOR ANY ELECTRICAL MACHINES?
What do you mean by an instrument transformer?
What is the function of NER and NET?
Discribe type of fault in DOL and stardelta startor.
What is electrical cable termination
What is transformation ratio what it describes?
What type of a DC motor would you use for a lift?
What is the temperature PROFILE OF A FLUID W. R. T. Distance from a sphere to which it is IN CONTACT which is at constant temp.?
why the neutral point in connnection oscillates?
If the rated speed of a d.c. Shunt motor is1440 r.p.m, which method of speed control would you suggested to obtain a speed of 1500 r.p.m?