How to select Main CB Rating for 220 KW Load?
Answers were Sorted based on User's Feedback
before the selection,first we should know that it is single
phase or three phase load.in case 1-phase we use p=vicosф to
find out the load current but in 3-phase we use p=√3vicosф.
suppose it's 3-phase then load current=382amp.now add
minimum 25% safety factor to it.then it will be 475amp ,so
we can select C.B of 500amp current rating.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / sennapparajan
for 220kw load curent is 380 amps. so your breaker should
be min 1.5 times of full load current. so u can select 630A
breaker.
Is This Answer Correct ? | 5 Yes | 3 No |
For the same power rating,which motor is bigger in size,AC or DC?
What should be the length of transmission line so that we can see/obtain the full sine wave of voltage??
What is a liquid resistance starter?where it is used??
Hello everyone, somebody knows what is a "surplice power" ? The hole phrase is: "This rating is appropriate for a generator set paralleled with an infinite bus e.g. a national electrical supply network or grid where the generator set is run at 100% load, 24 hours a day, 365 days a year and any surplice power is exported into the grid" Thanks in advance.
What is the fundamental cause of transients in power system?
How to Calculate Current Rating of SDFU (Switch Disconnector Fuse unit) for Protectionof Capacitor Bank connected to Busbar of 800Amp,in LV side of 11/0.433KV, 250KVA Transformer?
why dc did not flows to earth?
how caculate the pump head to maintain perticuler pressure of water and what would be the motor size in hp for the same?
When should I use earth leakage circuit breaker for incomer and when should I use it for each feeder seperately?
What is the size of a 60 watt and 80 watt tubelight?
if 11 lead acid batteries each 200 amph are connected in series so that combinly they can produce 110 volts dc. question is how much backup it can provide ? 2) how can we calculate that how much amprere and voltage is required to charge them . thanks in advance !
how many units (kwh) are there if in one MW?