Answer / guest

See the first thing is Power factor is angle between
voltage & current. see most of our load is inductive, & in
inductive load current always lags the supply voltage. In
unity P.f.condition current & voltage always in phase with
each other.
since P=VIcos(angle between V & I )
Now for a constant power as your pf changes i.e. decreases
to keep power demand constant current has to be increase as
your voltage is constant.in this way your current
increases , it causes increase in your copper losses
(I*I*R), voltage drop(I*R). And to keep voltage constant
more reactive power has to be provide.
generally any supply company penalties for more demand of
reactive power.

Is This Answer Correct ?    11 Yes 4 No

what happens if power factor is maintained at 0.9?give me the answer in technicall way rather than..

Answer / neo

The relation between the KW and KVA are

KW = KVA*Cos(phi)...SO as the power factor is getting lower
the actual outptut that we obtain frm a transformer will be
lower than the desired output for a particular value of
vlotage and current in that circuit.That is why in
industries, much importance in given for power factor
improvement.

Is This Answer Correct ?    4 Yes 1 No

what happens if power factor is maintained at 0.9?give me the answer in technicall way rather than..

Answer / hirosh babu

kw=kvacos(phi)... so larger the value of pf, smaller is the
amount of kva required for supplying active power... for
example if we require 8kw power output and pf is0.8 kva req
is 10.. but if pf is 0.5 kva req is 16... also for
transfering a const power if pf is low,... then value of
current will be high , so cu loss increases so does the
size of conductor..

Is This Answer Correct ?    3 Yes 0 No

what happens if power factor is maintained at 0.9?give me the answer in technicall way rather than..

Answer / hirosh babu

All the above answers are right. I just want to add few
points to that.

For transmitting a const power,

lower the power factor, greater will be the current and
hence greater will be losses and larger area of cross
section of conductor will be required.

By maintaining pf at 0.9, our active power will be high as
P= VI cos (pi), larger the pf larger the active power for a
fixed voltage and current.

Is This Answer Correct ?    3 Yes 1 No

what happens if power factor is maintained at 0.9?give me the answer in technicall way rather than..

Answer / badri narayan satpathy

If the power factor is .9 then we get a power loss.
Because power = volatse*current*cos phi(active power)
there for we also paid tha bill including the losses and
the losses is an usefullpower.power factor depend on the
type load like
inductive
capacitive
resitive

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

what are protective device needed to power a 360W ,50hz,240v,single phase,0.65 pf universal motor

1 Answers   L&T,


WHY BREAKER ARE USED IN SUBSTATIONS?

0 Answers   Fedco,


What are the loading factors to be considered for transformer sizing/selection?

3 Answers  


Why should be the frequency 50 hz 60hz only why not others like 45, 95 56 or anything , why should we maintain the frequency constant if so why it is only 50 hz 60hz?

0 Answers  


what do u mean by knee point voltage?

7 Answers   TATA,






Can anybody post questions asked in Engineers India Limited Interview? Thanks in advance.

0 Answers   Engineers India Limited,


what is LT & HT?

6 Answers  


our company have 750 kva oil transformer.still we have facing a problem that is when voltage is 11.5 kv coming from HT side then LT-side voltage is 420v or above at tape 1.please give me best solution to decrease the voltage

4 Answers   Gannon Dunkerley,


ELECTRICAL ENGINEER TEST IN FEWA ANY ONE HAVE KNOWLEDGE ABOUT THIS?????????

0 Answers  


How to reverse the direction of a DC motor ? By reversing the Armature wires or by reversing the field wires

2 Answers   KFC,


Fot testing new star-delta 132 kw motor in electrical worshop.we should check in star or delta connection as we do not have higher capacity cable in worshop?

4 Answers   Adani,


What will happened if the neutral of secondary of Xformer ( Star point) Note it's above KVA rated Xformer

0 Answers   Equate,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)