in three phase with neutral connection, what will happen,if
the neutral is in open condition with single phase
distribution panel
Answers were Sorted based on User's Feedback
Answer / m krishna
Simply your circuit is open circuit. No voltage appears
across your load. If your neutral is connected to ground at
panel end, then it behaves as before.
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / santosh kawade
If neutral is in open condition with single phase load, all
phase voltages will became unbalance, if load is lighting
load or home appliances there is high chances of lighting
bulbs will fuse or home appliances will burn.
Santosh Kawade
9224 69 3116
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / pillay
It depends where the neutral is in
open condition.
when all three phases are loaded with
single phase load and the main neutral
is in open condition than the voltage
across the load will vary according to
the load and the voltage can be as high
as phase to phase voltage thus resulting
in damage to electrical equipments, but
if they are loaded symmetrical than the
phase currents are balanced internally
and the voltage across the phases are balanced.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / jey
Whenever A neutral Gets open, The circuit Gets open and Voltage will be Unbalanced across the load
Is This Answer Correct ? | 0 Yes | 0 No |
what is the rating of Insulation tester for measure 15 KW, 3 phase 415V 50 HZ induction motor?
What is the function of Fuel and Oil filter in DG.
Does the ferranti effect has some impact on the electricity billing system on high voltage installations?
Which Motor used in Fan's Motor ?
3 Answers Matsui Technologies,
how to detect the presence of underground cable(while digging road)etc. -give the name of instrument
How would we calculate the no of earthing pits required for motor /panel
5 Answers APGenco, National Engineering Industries, Practical Viva Questions,
Why the substation measure in KV but not in the power ratings of transformer.
Can anyone provide with a SLD for HT panel installation for a 33KV line and distribution end has three 1.5MV transformers. Is it suitable to use OCB or VCB and also provide me the suitable rating and its connection diagram.
if harmonics is generates on the secondary side of transformer then why we put LC ckt on prim side?(i m talking abt rectiformer transformer)
how we can improove power factor?????????
Why rotating machines are not allowed to run near critical speed region?
HOW DO I CALCULATE THE SETTINGS FOR THE DIFFERENTIAL PROTECTION OF A 12kV/6.6kV, 6MVA,DYN11 XMER WITH PRIMARY SIDE CTR 400/1 AND SEC SIDE CTR 600/1?