While testing the 33KV Busbar by using Hipot kit, what
should be the test voltage we have to apply
Answers were Sorted based on User's Feedback
Answer / ramaswamy venkatachalam
At the factory, it is tested by applying twice the voltage.
ie, 2U. If a dc kit is used, (2U)/sqrt(2) + 1 KV. Which is
a minimum of 48 kV. You can use 50 kV test kit for the same.
Convert the ac rms voltage to dc by dividing by sqrt(2) and
multiplying it by 2 and adding 1kV to it.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / gunaskaran
for ac 0.8(2E+1) normally we r doing in ac if customer
asking we can do the dc for DC (2E+1*1.414)0.8 this 1.414
is AC to DC conversion this for site for factory we have to
applie 100% voltage
Is This Answer Correct ? | 1 Yes | 3 No |
we specify current in case of feeder but in case of distributor voltage, why?
use of choke in APFC panels
short notes on npn & pnp transisitor..........
What is dynamo?How it works and what is the function of dynamo in a DG.
What are objectives of energy managements ?
i will applied in 1U-1W on 440 volt primary delta side. what is the result of magtic balance test
How much costly in percentage wise is sandwich busduct costly than air insulated busduct of any rating?
What are the disadvantages if neutral current exists in grounded star transformer distribution system?
If any cable burnt how can we identify it burnt by high current of high voltage?
how to calculate the change over time for star delta starter for different KW motor?
what is the difference between the following 2 situations ? 1)Line & Neutral=240V Line & Earth=230V Neutral & Earth=10V 2)Line & Neutral=230V Line & Earth=240V Neutral & Earth=10V
what are the changes made in induction motor so that it act as induction generator