Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why transformer is rated in KVA ?

Answers were Sorted based on User's Feedback



why transformer is rated in KVA ?..

Answer / gajanan

there are two losses occure in transformer viz. Cu loss and
iron loss.
Cu loss depends on current & iron loss depends
on voltage and not affected by power fector hence always
transformer ratting defined in KVA not in Kw.

Is This Answer Correct ?    21 Yes 3 No

why transformer is rated in KVA ?..

Answer / prabahakaran

WE know the relation of power in three phase =
&#8730;3VIcosØ.hence we can say that the load is not constant it
very accordingly. So power factor is also get vary with
load it is hard to define the power of transformer so it is
rated in KVA.

Is This Answer Correct ?    2 Yes 2 No

why transformer is rated in KVA ?..

Answer / gaurav bhardwaj

Rating is any device,s power capacity..so if u know how much useful power u can get then only it will be in kW..bcz power factor plays role in useful power then we can say that if a transformer has 20kva rating then it will deliver 20,kw at pf=1..Nd as we don't know the load which is to be supplied that's y rating in kva ,as kW=kva*pf

Is This Answer Correct ?    0 Yes 0 No

why transformer is rated in KVA ?..

Answer / eng. d

I like the answer which is talking about the cu losses and
characterstic of the transformers.

let me drive the answer from differint angle.

let us assume that we told you that, the transformer is 20
MW, and now you want to connect motor of 15 MW to this
transformer, are you able to start this motor from this
transformer before the protection setting trip the circuit
breaker of the transformer?

I don't really know!! because I don't know how much
reactive power in this transformer, in other words, I don't
know how much losses in this transformer, then I can't do
prpoer analisys of the motor starting without knowing the
MVA rating.(which will include active and reactive power)

my advice, please try to do motor starting analysis on ETAP
or Matlap or any electrical softwaer and play with the
reactive power and see the differance and you will be clear
more ^_*
good luck

Is This Answer Correct ?    1 Yes 2 No

why transformer is rated in KVA ?..

Answer / chinna

trf rating in KVA,current measures in amps&voltages
measures in volts.thats trf rating in kva.

Is This Answer Correct ?    4 Yes 11 No

Post New Answer

More Electrical Engineering Interview Questions

what is the difference between line & phase current in star delta connection motor?

2 Answers  


what is skin effect and why is it absent in DC systems

4 Answers  


what is tha gap between the pole of 132kv line

2 Answers  


How we calculate the size of H.T cable for any transformer & rating of busbar for any L.T. panel?

3 Answers  


how we are measuring the import and export power?

1 Answers  


what is the operating principle of contactor(power).along with disection?

3 Answers   NASA, Tech Mahindra,


What are operating procudures & Safety precautions to be observed while operating OLTC in manual mode ?

0 Answers   NTPC,


how can we represne the analog signal and digital signal if want to measure the speed and we have to use PLC

2 Answers  


what is the difference in operation of 3 phase motor when am forward delta connection and reverse delta connection?

1 Answers   Birla,


What is the minimum underground tank size capacity considered for firefighting purpose?

0 Answers  


condition Autotrip facia come on control panel of electrical transmission line?

0 Answers   Getco,


The DC current waveform is - . What about the fire alarm waveform?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)