Is there any problem if i connect APFC panel in generator
circuit
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
APFC is employed when the gen is connected to grid and the
grid voltage is continually fluctuating,so that the pf
remains constant, as otherwise the operator has to vary the
excitation every now and then.But with this mode gen voltage
may rise if the grid fails.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
I mean APFC mode of the excitation system not the one with
capacitors.
Is This Answer Correct ? | 2 Yes | 0 No |
Why 1/3 is used in symmetrical components?
why reactive power control is required
what is compatible kva for 3300 watts and why
What is the exact formula for one weber of magnetic flux?
for preparation of design note of 11 / 220 kV , 3 phase, 63 MVA transformer how can calculate or consider the iron losses and copper losses
What are the advantages of speed control using thyristor?
list of tests to be carried out at manufacturers end while purchasing a step up transformer of 11kv to 66kv ,2MVa Capacity.
what is the advantage of Cathodic eathing system and what is the basic principle and how itis working, please explain clearly .
what is the Connected Load (kW) or Contract Demand (kVA)of mahindra nasik plant??
Why do not we prefer non conventional sources of energy to conventional sources?
At 765Kv, I have seen the use of PT at line side for metering and CVT for protection, although as far as my knowledge is concern, PT at this voltage level will have huge loss and more cost as compared to CVT as CVT can also perform same function of Protection and Metering? So my question is why use PT and not CVT for metering and protection in order to reduce the cost.
why power generated only 11KV not more than???????? and why power up/down is multification of 11*?=??.??? foe Example 11/33,11/66,66/11KV etc,