A Generator is in running condition and Rotor earth fault
alarm is coming.How to check on line(i.e in running
condition) whether there is actual earth fault in rotor or
not.
Answers were Sorted based on User's Feedback
Answer / kk
Rotor earth relay have 2
stage. One 4 alarm & other 4
trip. One can check the
bridge o/p voltage(mV) &
compare with comissioning
time value.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / bhuvnesh kumawat
rotor earth fault alarm comes only if our carbon brushes
become earthed. it may be at the time of changing carbon
brushes.
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / sujeet kumar
we have to check the status of zero sequence relay..
if its not affected then there is not any earth fault
Is This Answer Correct ? | 0 Yes | 5 No |
Answer / alok
rotor both side earth fault wire open and check countinuti
with the help of multimeter at rotor both end.but one side
wire who is grounded must be grounded.
Is This Answer Correct ? | 2 Yes | 8 No |
What accessories required to give the motor with given circuits and do you know the ratings of those accessories?
How shall i design a liquid rotor starter
What is the tests required for a 132 kV, 400 kV , 765 kV for a Circuit Breaker and Power Transformer before commissioning ?
0 Answers Eprosys Engineering Consultants,
Three phase alternators are connected in star connection why?
Mr. mohh sahid m not satisfied for ur answer to the que weather the size of transformer increases or decreases withchange in fr for more detail go to the answer given by me
why high current produce in case of transformer when turns are internally gets shorted.
In a distribution system,having 3phases & 1 nuetral.ecah phase to neutral is 230V,line-line voltage is 440V,but what is the voltage of each line.but it should obey the KVL law.
What is the difference between diode and a transistor in terms of the direction of current flow?
Why single phase induction motors are not self starting ?
you have a 2 tonne ac that operates for 2 hrs daily what will be you monthly bill (this is complete question asked nothing else was given)?
A 400KVA ,50HZ TRANSFORMER IS TO BE OPERATED AT 50HZ.THEN KVA RATING OF THE TRANSFORMER?.
WHAT IS M.P.C.B