A Generator is in running condition and Rotor earth fault
alarm is coming.How to check on line(i.e in running
condition) whether there is actual earth fault in rotor or
not.

Answer Posted / kk

Rotor earth relay have 2
stage. One 4 alarm & other 4
trip. One can check the
bridge o/p voltage(mV) &
compare with comissioning
time value.

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

TRAFO 1. WHY BREATHER IS USED. 2. WHY OIL GOES DOWN IN CONSERVATOR TANK. 3. WHY WE ARE TAKING OIL SAMPLE TAKING FROM BOTTOM OF TRANSFORMER. 4. HOW TO CHECK IR VALUE OF TRANSFORMER. 5. WHY OLTC HAVING BUCHHOLZ TRIP ONLY; WHY NO ALARM. 6. OFF LOAD TAP CHANGER OPERATION PROCEDURE. 7. TR. SHUTDOWN / ISOLATION PROCEDURE. 8. WHEN THREE TRS. IN PARALLEL, ONE TR. IS NOT SHARING THE LOAD – WHAT IS REASON AND WHAT YOU WILL DO. 9. WHY TR. HAS OLTC IN HV SIDE. 10. WHAT IS % IMPEDANCE. 11. WHY TR. RATING IN MVA. 12. WHAT IS VECTOR GROUP IN TR. 13. CONDITION FOR PARALLEL OPERATION OF TRS. 14. WHAT IS TERTIARY WINDING. WHERE IT WILL BE. 15. IF TR. TRIP ON BUCHHOLZ OR TAP CHANGER RELAY, WHAT YOU WILL DO. 16. DIFFERENCE BETWEEN OIL TEMP. AND WINDING TEMP. PROTECTION 17. HOW WINDING TEMP. IS MEASURED IN CAST RESIN TR. 18. DIFFERENT TYPES OF FAULTS IN TR. Trafo - Page-1 of 2 19. WHAT HAPPENS WHEN TR. CHARGED FROM LV. 20. WHAT WILL YOU DO IF MEGGER READING SHOWS ZERO BETWEEN LV WINDING AND EARTH. 21. CAN WE INTERCHANGE BUCHHOLZ RELAY OF MAIN TANK AND OLTC TANK. 22. IF THE LINE BETWEEN BREATHER AND CONSERVATOR TANK 23. LOCKED, WHAT WILL HAPPEN DURING LOAD CYCLE. 24. WHAT IS THE FUNCTION OF OIL SEAL IN BREATHER. 25. WHAT ARE LOCATIONS FOR BUCHHOLZ RELAY FIXED IN POWER TR. 26. WHAT ARE CHECKS IN POWER TR. DURING MAINTENANCE. 27. WHAT IS IMPORTANT WHEN WE CHECK OLTC OPERATION DURING MAINTENANCE. Trafo - Page 2 of 2

1999


What is the difference between a 3 winding and 2 winding Potential Transformer

1816


How can we convert 11 kv to 440 volt without using transformer ?

979


a 100mva,400/200v transformer has leakage impdce of 10% draws a steady state line currentof---------------

1454


What is time invariant system?

681






If more than rated DC voltage appears across trip coil of the breaker, what will happen? e.g. in 110V DC circuit system, if voltage across battery terminal showing 121 V

1191


How you give clearance to a spare feeder.

1214


what is the solution for meger test failed the MV cable?

3523


difference between a diode and thyristor?

1765


how can maintaince the acb contactor moveing and fixing kit

1585


I NEED RRB APTITUDE QUESTIONS AND MODEL PAPER,PLEASE SEND MY E-MAIL joo28_eee@yahoo.co.in

1452


what are different types of electrical windings? i know the distributed winding ,concentrated winding etc but i want some detailed information, in what condition we will use distributed,concentrated windings what are the difference between them which is best, how induced emf changes by using different types of windings 20 hours ago - 1 week left to answer

1518


Briefing the effects of ASR and ACR of a double closed-loop speed regulating system.

1694


what is difference between 9kv 5ka surge arrester and 9kv 10ka surge arrester.

1403


What is the reason for using a GE G101 MCB in place of an EP102 MCB if both are capable of AC circuit protection?

2150