What happens if the capacitive reactance of a transmission
line is very high?
Answers were Sorted based on User's Feedback
Answer / prashant singh
when capecitive reactance of transmission line is high then
more charging current will flow through line rhen losses
will increases. and due to capecitive effect reciving end
voltage high the sending end voltage. and voltage
distribution is goes unequal.
Is This Answer Correct ? | 46 Yes | 4 No |
Answer / richa
when capecitive reactance oftransmission line is high then
voltage is high ta the receving end
Is This Answer Correct ? | 20 Yes | 2 No |
Answer / akshay dhar
This effect is prmarily known as Ferranti effect & due to which the receiving end voltage will be greater than the sending end voltage (abt 5-10% of Vs)
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / subhani
when capecitive reactance oftransmission line is high then
the power factor of the system will increase.sometimes it
may lead to ferranti effect also...
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / abhishek kunwar
when capacitive reactance of transmission line high then
high charging current will flow through line.due to leading
effect losses are increase.and this will inject the voltage
from receiving end and at receiving end voltage level increase.
Is This Answer Correct ? | 1 Yes | 2 No |
I have an 15A fuse MCB that controls a night storage heater. It needs replacing and is now obsolete. Is a 16A C curve MCB the correct replacement?
on 22.03.2015 at 17:15hrs Y phase 66kV class Power Trf-2 Current transformer has flashed over and oil came out. The failed CT has been replaced on 24.03.2015 at 13:15hrs and the Trf has been charged in presence of RT Hassan after conducting the pre-commissioning tests. On the same day at 17:00hrs the commissioned CT has again flashed over and immediately the Trf has been isolated from power supply. It is confirmed the secondary is not opened and checked the earth integrity and is found ok. Here what would be the reason for the CT failure?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
why we used stone chips under the transformer area..
Why using synchronising methed in DG's sets?
give single line diagram of D.G distribution form alternator to main L.T panel?
What is the role and reponsibilities of Electrical Engineers in construction field?
12 Answers ETA, Garg Electronics, L&T,
Define relative stability.
Explain the terms real power, apparent power and reactive power for ac circuits and also the units used.
how to distinguish between ac motor and dc motor without seeing name plate of it.only seeing its getup look
at what basis/standard we have to arrive the current density of aluminium/ copper in busbar?
what is the difference between main meter CT and check meter CT?and what is the difference between main meter PT and check meter PT?