the distance from my office to d.g is aprox 400mtrs and
voltage drops ibn my office near about 40 volt what should
i do p[ls suggest.
Answers were Sorted based on User's Feedback
Answer / sabale.dnyanehswar@gmail.com
IF U ASKING ABT DC Voltage then ans is
1. u have to increase the sq.mm size of the cable. i.e if
u r laid cable size is 16 sq.mm. u can go to 25 sq.mm.
2. u have to increase u r battery Amphour rating . by
replacing it with higher rating.
if u asking abt AC voltage:
1. check the DG set terminal voltage if voltage is not
proper then check at AVR terminal. if there also not ok.
then check it with another AVR card.
2. if AVR is OK then check any leakage of cable with taking
megger & continuty with earth.
3. if problem is found in cable then replace with new one
or increase the rating of cable.
if everythink is ok. then take voltage at receiver end with
out load. one by one increase the load at every time
voltage reading. if found prob. in another ckt. rectify it.
The range should be +- 5% should be accepted.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thowsif
Hi ,
Go through this link:-http://www.psihq.com/iread/faqvolt.htm
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / amit chaudhary
You should check the cable size which you are using from
your office to DG set. May it will need to increase the size
of cable.
If you are not using this DG set for another purpose then
you can increase the generator voltage by AVR to get the
suitable voltage in your office.
If the cable is heated during the load then you will have to
increase the cable size.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raj
Above all answers are right but one more we can do is to
add capacitor at load end to increase the voltage.
| Is This Answer Correct ? | 0 Yes | 0 No |
whats happen if we disconnect the NGR of alternator in running condition?. Generally we observed that transformer netrul is directly grounded but alternator connected with NGR, then ground?
what is the role of transistor in Circuit?
what is EBXl (electron beam cross linked ) cable ?
in case of transformer the power factor is depend on input or the output
diff b/w normal grounding and resistance grounding
sir i have applied for isro-09. still i did not got the HALL TICKET.
what is defference by mcb,mccb and mpcb
Difference between online and offline UPS?
what is insulation percentage of motor 3 phase and singlephase
what is cogging and crawling
20 Answers ABB, Ashok Leyland, Bharat Bijlee, BMRCL, MN Dastur, Siemens,
how the length effects the ampacity of the cable? if a cable is carrying a current of 100A for 50m length then what will the effect on current if we double the length?
why there is a temperature rise at different metal to metal contact at cable lug??suppose cable is aluminium and the lug is copper,than why the temperature rise takes place??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)