the distance from my office to d.g is aprox 400mtrs and
voltage drops ibn my office near about 40 volt what should
i do p[ls suggest.
Answers were Sorted based on User's Feedback
Answer / sabale.dnyanehswar@gmail.com
IF U ASKING ABT DC Voltage then ans is
1. u have to increase the sq.mm size of the cable. i.e if
u r laid cable size is 16 sq.mm. u can go to 25 sq.mm.
2. u have to increase u r battery Amphour rating . by
replacing it with higher rating.
if u asking abt AC voltage:
1. check the DG set terminal voltage if voltage is not
proper then check at AVR terminal. if there also not ok.
then check it with another AVR card.
2. if AVR is OK then check any leakage of cable with taking
megger & continuty with earth.
3. if problem is found in cable then replace with new one
or increase the rating of cable.
if everythink is ok. then take voltage at receiver end with
out load. one by one increase the load at every time
voltage reading. if found prob. in another ckt. rectify it.
The range should be +- 5% should be accepted.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thowsif
Hi ,
Go through this link:-http://www.psihq.com/iread/faqvolt.htm
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / amit chaudhary
You should check the cable size which you are using from
your office to DG set. May it will need to increase the size
of cable.
If you are not using this DG set for another purpose then
you can increase the generator voltage by AVR to get the
suitable voltage in your office.
If the cable is heated during the load then you will have to
increase the cable size.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raj
Above all answers are right but one more we can do is to
add capacitor at load end to increase the voltage.
| Is This Answer Correct ? | 0 Yes | 0 No |
difference between ordinary MCCB & Motorised MCCB
What is the equipment used to control the generator output?
how to calculate full load current of transformer & induction moter ?
My load is 1635 KW. & current pf is 0.884, I have to improve it for 0.99.Please suggest what KVAR value is needed?
. What should be the minimum and maximum ohmic value for earthing?
How to test the vector group of a Yd11 transformer? what are the relations to be checked between various vectors to confirm this vector group?
A resistance, inductance & capacitance are connected in series between points A & B.The voltage drops across the resistance,inductance&capacitance are found to be 40V,70V&100V respectively. What is the total voltage between between points A&B (Vab)? a)210V b)70V c)50V d)230V
why the carbon brushes are used heat created rotating parts in eiectricity
For backup batteries connection,which method is best? series or parallel ?
what is meant by 3rd hormonics ?
For example, if I use Star delta transformer for distribution, Can I Connect 230 V lighting load bewteen secondary phase & primary neutarl. What will be the effect, if I connect in this manner?
Why the power generated in dams is complex power? Why the generators in dams cannot produce Real power directly (i.e power which has zero reactive part)?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)