what is the meaning of reverse action and forward action of
control valve...
Answers were Sorted based on User's Feedback
HhHHH
Hi my dear friend the valve action depends on the
service.If the PV increasing the valve opening also
increasing, the action is direct action.If the PV
increasing, the valve opening decreasing i.e reverse action.
For example if you used one valve to fill the tank.if the
PV increasing, you have to close the valve.i.e your valve
action is reverse to the PV value.
If you used valve in discharge line of the tank.If the PV
increasing, you have to open the valve. i.e your valve
action is direct to the PV value.
SP-PV=Error=Reverse action
PV-SP=Error=direct action
| Is This Answer Correct ? | 33 Yes | 6 No |
Answer / hvkkumar,mtech instrumentation
for pressure increases the % of valve opening increase in
direct action .but in case of reverse actoin pressure
increases the % of valve opening decrease.
| Is This Answer Correct ? | 27 Yes | 11 No |
Answer / alexpandian
Hi,
We r using direct&reverse actuion in many places:
Control vlv- By giving air, if the stem of actuator moves
down then its dircet acting actutor & if stem moves up then
it is reverse acting.
Controller-
DIRECT: If the PV is less than SV then MV will
decrease.Mainly using in vent valve application.
REVERSE; If the PV is less than SV then MV will
increase.using in normal control loops.
PV-process value SV-set value MV-manipulated value
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / saravanan
Direct acting valve
Air to close -- Spring to open --- Failed Open (FO)
(increasing air pressure pushes down diaphragm and extends
actuator stem)
Reverse acting valve
Air to open -- Spring to close --- Failed Close (FC)
(increasing air pressure pushes up diaphragm and retracts
actuator stem)
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / j arumugam
if control variable(CV) INCREASES process variable
INCREASES is called Direct acting (Gain < 0)
if control variable(CV) INCREASES process variable
DECREASES is called Reverse acting (Gain > 0)
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / naganaresh katta
If PV>SV then MV Increases in direct action
IF PV<SV then MV Decreases in reverse action.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / www.islamqa.com
For linear motion valves
Direct acting valve:
====================
valve opens when stem is drawn out of the body
Reverse acting valve:
=====================
valve closes when stem in pushed into the body
reference:
Lessons in industrial instrumentation - version 4 - page:713
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
CELL.: 00 2 0121367310
| Is This Answer Correct ? | 6 Yes | 9 No |
Answer / vinayak
Hi ...
Revese action normally used in AIR Fail to Close valve.
Direct acttion normally used for Fail Open valve.
It is very important to define reverse or direct action as
per process requirement.
DIRECT ACTION :
20 MA DC = 0 % VALVE CLOSE
16 MA DC = 25 % VALVE OPEN
12 MA DC = 50 % VALVE OPEN
8 MA DC = 75 % VALVE OPEN
4 MA DC = 100 % VALVE OPEN
REVERSE ACTION :
4 MA DC = 0 % VALVE CLOSE
8 MA DC = 25 % VALVE OPEN
12 MA DC = 50 % VALVE OPEN
16 MA DC = 75 % VALVE OPEN
20 MA DC = 100 % VALVE OPEN
| Is This Answer Correct ? | 8 Yes | 11 No |
REVERSE ACTION CV = AIR TO CLOSE = AIR FAIL TO OPEN
DIRECT ACTION CV= AIR TO OPEN =AIR AIL TO CLOSE
| Is This Answer Correct ? | 20 Yes | 31 No |
What are the characteristics of Control Valve
What is the maximum distance limit of 4-20mA and 0-10V DC standard signal transmission ?
why we r opening HOT BYPASS valve during startup of a compressor?
which gas or which liquid is filled in capillary of dial type temperature indicators on power transformers
can we use a control valve without positioner
IS IT POSSIBLE TO CALIBRATE A LEVEL TRANSMITTER INDICATOR(ABB) USING HART COMMUNICATOR.? I MEAN TO CHANGE FROM ONE UNIT TO ANOTHER WITHIN INDICATOR (EG. INCH TO FEET)...? PLZ NOTE THAT I HAVE MADE THE UNIT CHANGE IN TRANSMITTER USING HART COMMUNICATOR..BUT WHAT ABOUT THE INDICATOR..?
explain the working of Coriolis Flowmeter.
How Honeywell FSC is functioning and what is its purpose? Can we bypasa it and only use DCS instead of that.
how we can measure the interface level?is it possible to measure interface level with dp or pressure transmitter?
Close loop and open loop.
How can test or measure the probe and extension cable to identify if the problem at the probe or cable or at the driver it self? (pleast notify the measuring method)
What is first echo & echo window in radar type level transmitter?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)