Is it possible to use AC supply insted of DC supply in trip
coil operation? if not, why?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The plunger will not act with AC supply
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / linish
Trip circuit should be powered from a class 1
supply since it is responsible for
total protection of the system,so most reliable
source will be battery that is DC
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / vvvv
a trip coil is expected to work with high speed reliably so
as to produce effective jurk.
AC supply can also be used for trip coil subject to proper
design. however after comparison for same rating coils, it
will be clear that DC Trip coils exhibit the required
performance as compared to AC
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / thanigai1984
We cant store the AC supply... we store only DC supply ...when abnormal condition AC supply will Trip on that time we used as DC supply .. that why they use DC coils for Trip and Close..
| Is This Answer Correct ? | 3 Yes | 2 No |
Main reason is property of Inductance.
| Is This Answer Correct ? | 1 Yes | 0 No |
how much winding resistance of 0.75kw to 12.5kw 3ph sqwiralcage induction motor?
What is the one main difference between ups & inverter ? And electrical engineering & electronics engineering ?
why dc source used for HV breakers and Relays operation?
In both 600/1000 V cable and 450/750 V cable, we can supply 415 V. However for distribution, all utilities are using only 600/100 V instead of 450/750 V. What is the reason?
What is encoder, how it function
What is restricted earth fault protection ?
how to find diesel consumption of 600kva DG per hours????
i want to learn control schedule for 11kv panel? can any one send the detailed control schedule?
Why Humming noise originated in Starter motor and how it was generated ?
state types of reflectors in illumination engg. ???????
ohms law aplicable
For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply was applied at the HV. Connection between Aa was made with a 2.5mm cable. As soon as power was switched on the cable caught fire and burnt. This test was then abandoned. It is noteworthy to say that a similar cable was also used in a similar transformer for the same. The cable did not burn and test was successfully completed with good result. What is wrong? Please, help me out.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)