what is the difference between Miniature circuit breaker &
motor control circuit breaker ?
Answers were Sorted based on User's Feedback
Answer / shantanu dash
Miniature Circuit Breaker (MCB)has less short circuit with
stand current than MCCB( Moulded Case circuit breaker) or
MPCB( Motor protection Circuit Breaker).
Exp. MCB has short circuit withstand capacity of max. upto
10 KA. But MCCB/MPCB has fault withstand capacity from 25
KA to 50 KA or more.
Miniature circuit breaker comes in single pole/ two
pole/three pole/Four pole versions. but MCCB comes in
three/four pole version and MPCB comes in only three pole
version.
MCB Normally used in the lighting circuit. But MCCB is used
for feeder as well as motor protection having
Overload/short circuit/ earthfault protection in conjuction
with an additional over load relay. MPCB is only used for
Motor Protection.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / soumya chatterjee
First of all if you want to mean MCCB please read Moulded
Case Circuit Breaker not Motor Control Circuit Breaker.
MCCBs are superior than MCB by virtue of its higher short
time current withstand capacity.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / winner
MOTOR CONTROL CIRCUIT BREAKER(MCCB)IS MORE SENSITIVE THAN
MINIATURE CIRCUIT BREAKER(MCB).IN MCCB THE SHOT TIME
WITHSTAND CAPACITY IS HIGHER THAN MCB.THEN MCCB COST IS
HIGHER THAN MCB
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / gunasekaran
first one is automatic second one is relay oriented
| Is This Answer Correct ? | 3 Yes | 4 No |
What is the function of pulse transformer?
what's the difference between ATS and AMF...??pls answer me in detail with its working principle and construction also..
Why Magnetic Core Balance test is performed only on Star side of Transformer and not on Delta Side of Transformer (Vector Group Dyn11)?
. How to calculate the Short Circuit Impedance in Transformer? How to calculate the Short Circuit Impedance in Transformer?
what are the differences between MCB and MCCB ?
19 Answers Bhel, DLF, Omax,
How to calculate or formula to calculate rhe power in 2 phase system ??
we are having 110 Kv,250mA Electrostatic precipitators for coal fired boilers. what will be static voltage and current after discharge and what time it will remain before earthing?
WHY THREE PHESE SYSTEM VOLTAGE APPLIED IN 440 VOLT
Describe the control mechanism of missile launcher???
What is the method of Tan delta test for power Transformes and why it is required.
in three phase circuit neutral failure what happend in homes
wat is the need of capacitor on aceiling fan?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)