the humming noise is due to the MAGNETOSTRICTION phenomenon.
the magnetostriction is caused due to the quik magnetic
reversals in ac circuit. magnentostriction is developed from
the words 'magnetic' 'restriction' implies the opposition of
the reversals of the magnetizing current.or simply..
oppozing the magnetizing and demagnetizing processes..
due to this some energy is lost in heat and some enrgy is
lost inthe form of sound but notice that sound was aktualy
produced by the minute vibration of the core and some other
metal parts. but we cant see this vibration wth our naked eye.
generally megentostriction does not okkurs in dc ckts.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / amit
humming noise is a sound produced in power transmission line during the transmission of power.it is produced due to corona effect.it can be supresed by using stranded wires..
| Is This Answer Correct ? | 0 Yes | 0 No |
In 3 phase induction motor 1hp current rating is 1.5 amps constant ? is correct or not ?
How can we calculate the fault level of the distribution system knowing the percentage impedance of transformer & subsequent equipments.
we have two generators different capacity on 15 MW and other 6MW at 11 KV , 15 MW gen. bus short level current 40KA,and 6MW short level current 25KA,, length of cable 100MTR between 6 MW from 15MW gen. for bus coupling . kindly tell any one can we use both NGR OR one NGR from any GEN. BOTH NGR has diff. rating. Tariq pakistan
what is battery impedance testing and how we perform this test with four wires.
A copper wire of length l and diameter d has potential difference V applied at its two ends. The drift velocity is vd. If the diameter of wire is made d/3, then drift velocity becomes
What are the circuit models used for analysis of medium length transmission lines? Which one is superior? Support your answer.
We are using 4 MVA transformer and we provided 2 separate earthing pit for Body and 2 separate earthing pit for neutral, can we connect separate body earthing pit to other earthing pit (Equipment earthing)?
dear all, in motor operation , motor is of 100 hp and bimetal relay setting is 130 amp, if relay is getting tripped on 120 amp balance current what can be the reason? Relay is newly replaced. I dont know but is there any frequency effect in thit case? Can frequency variation affect bimetal relay operation?
In an panel board if the outgoings are power plugs and motor equipments...what should we choose as the incomer of the of the panel board?? MCCB OR ISOLATOR?? Should we use ELCB protection??if so where??
What should be cable size for 75KVA 380/220 3ph transformer
to operate air conditioner of 1.5ton what power of generator is required
how many parameters can integrate with fire alarm basically ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)