How can we calculate the current if we have load in KVA and if
the load in KW then what formula will be use for calculating
the current. please give both the formula for calculating the
current.
Answers were Sorted based on User's Feedback
For KVA rating,
The formula for determine the current is:
I = KVA/(1.732 x Voltage) (For three phase system)
I = KVA/Voltage (For Single Phase)
For KW rating
The Formula for current is
I= KW/(1.732 x Voltage x Power factor)(for three phase system)
I = KW/(Voltage X Power factor)(For Single Phase)
| Is This Answer Correct ? | 20 Yes | 2 No |
Answer / j.l. singh
If there is three phase system formula for the
KW = 1000.root3 VA cos Phi.
KVA = 1000 VA
V =Voltage A = Ampere.
| Is This Answer Correct ? | 19 Yes | 7 No |
Answer / denzel101
For KVA rating, the formuler for current will be:
I = KVA/(0.707 x Voltage) for three phase system
For KW rating
I= KW/(0.707 x Voltage x cos phi)
for three phase system
| Is This Answer Correct ? | 5 Yes | 17 No |
one cable insulation resistance 200 mega ohm. how find 250 meter cable resistance.
why we test the core balance of the transformer?
In case of generator when we consume more power produces by it why load on generator increase and starts sound more. and how it is adjusted..
what is meant by motor protection relay & its working principle ?k
what happens if number of poles in stator and rotor windins of slip ring induction motor are not same. Will it rotate near to the synchronus speed defined by stator?
how the transformer stables out zone faults? Because we use non directional O/C relays .Is there any special considerations are taking into account to overtake this?
Thermal withstand capability under full short circuit conditions, in terms of number of times of occurrence of short circuit and corresponding anticipated percentage reduction in transformer life.
What are the conditions to be satisfied for parallel operation of dc generators?
why choke is provided in the centre of the tube light?
If the capacity of water Tank is 50000 Liters situated at 20 meters height from ground level,What would be the size of pipe and how much USGPH water will be supplied and what will be the motor or pump rating used for this work?Illustrate by showing formula?
Why is shaft current insulation required on large motors & when should it be checked i.e. before or after assembly?
why sielent pole is used only in hydro generators and not in turbo generators
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)