How can we calculate the current if we have load in KVA and if
the load in KW then what formula will be use for calculating
the current. please give both the formula for calculating the
current.
Answers were Sorted based on User's Feedback
For KVA rating,
The formula for determine the current is:
I = KVA/(1.732 x Voltage) (For three phase system)
I = KVA/Voltage (For Single Phase)
For KW rating
The Formula for current is
I= KW/(1.732 x Voltage x Power factor)(for three phase system)
I = KW/(Voltage X Power factor)(For Single Phase)
| Is This Answer Correct ? | 20 Yes | 2 No |
Answer / j.l. singh
If there is three phase system formula for the
KW = 1000.root3 VA cos Phi.
KVA = 1000 VA
V =Voltage A = Ampere.
| Is This Answer Correct ? | 19 Yes | 7 No |
Answer / denzel101
For KVA rating, the formuler for current will be:
I = KVA/(0.707 x Voltage) for three phase system
For KW rating
I= KW/(0.707 x Voltage x cos phi)
for three phase system
| Is This Answer Correct ? | 5 Yes | 17 No |
what is frequency? and its importance
why we use Bus earth truck and Cable earth truck
What if high voltage side circuit breaker of a ehv transformer instead of lvcb? Kindly elaborate.
0 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
What is basic fundamental for choosing NGR or NGT for any generator neutral grounding
what is booster? and how it is connected in a circuit?
How to design the NGR Resistance
How i can decide that HVDC line is best for transmission.
what is the function of a circuit breaker ?how does the circuit breaker function during normal operation of an electrical system
upto how much low RPM we will run the commercial motor which is run through VFD without any problem occurs in motor.Motor rating Duty is S1 & RPM is 1400.
how i run d.c. moter with solar panel without use of battery?
In a 3Ph induction motor(old) 6 wires came out from terminal & not mentioned u1,v1,w1,u2,v2 & w2. how can find out the terminals? how can connect to star delta starter??
I have a 25kVA three phase transformer on our property. Will this transformer be large enough to run a large home with swimming pool, spa, 2 off full size reverse cycle air conditioners to service a 100 square house (10,000 square feet or 930 square metres)and the general power consumption of this house without upgrading to a 63kVA transformer.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)