How can we calculate the current if we have load in KVA and if
the load in KW then what formula will be use for calculating
the current. please give both the formula for calculating the
current.
Answer Posted / soumen das biswas
For KVA rating,
The formula for determine the current is:
I = KVA/(1.732 x Voltage) (For three phase system)
I = KVA/Voltage (For Single Phase)
For KW rating
The Formula for current is
I= KW/(1.732 x Voltage x Power factor)(for three phase system)
I = KW/(Voltage X Power factor)(For Single Phase)
Is This Answer Correct ? | 20 Yes | 2 No |
Post New Answer View All Answers
for 750 kw LT load what will be the ht kva
what questions are asked in the interview for the post of an electrical maintenance engineer in FMCG companies?
i need about 10 years of GATE solved papers in pdf format and even mock tests toooo
Is it acceptable of installing an earth pit in planters area where bare copper cable, earth rod and connection are susceptible to corrosion due to water?
why we get 2 differnet values for power factor in 2 watt meter method in 3 phase
what is the difference b/w ground & virtual ground?
Saving in copper achieved by converting a 2 winding transformer in to an auto transformer is determined by A voltage transformation ratio B load on secondary C quality of core material D size of transformer core
List the characteristics of filter?
What are the functions of temperature scanner in power transformer?
What are the causes for the failures of sandwich type (Al) busducts?
in dc series motor if field wdg is shorted then
In electrical what is earth(ground)connection, wht is the importance of it, why it is recomended to maitain below 3VAC between Neutral and earthspecially in PLC used machines?
how much maximum load a 2 core (Single phase) 16mm aluminium wire can take ?
I want to know how to calculate the size of electricity cable in building?
why we permissive overreach in distance protection.where it is applicable to use in long r short lines