WHY TRANSFORMERS ARE RATED IN 11KV 22KV 33KV Instead off
10kv 20kv 30kv
Answers were Sorted based on User's Feedback
Answer / bala123
Because the Form factor of AC system is 1.11,thats why the
voltage rating from the transformer was above format
Is This Answer Correct ? | 83 Yes | 10 No |
Answer / syam kumar
beacuse Tranformer output voltage is given by the equation
E = 4.44f(phi)N
so Voltages are multiples of 1.11
Is This Answer Correct ? | 32 Yes | 6 No |
Answer / vipul mali
because form factor is definded by
ff= r.m.s. value/average value
ff= 1/root 2/ 2f/ pi
ff= 1.11
so all the equipments are disigned with this value.
Is This Answer Correct ? | 20 Yes | 6 No |
Answer / eng_entropy
Because these values of voltage are the standard values
which produced by the generators.
Is This Answer Correct ? | 5 Yes | 47 No |
are induction motor have poles? yes / no , why?
What is meant by shunt current?
what is the difference between interconnection and intraconnections in the circuit diagrams
In HT overhead line why should provide top conducter which is not connected whith insulater..?
a)In a 3-phase 4-wire circuit, a circuit breaker is selected to protect the circuit whose highest fault level is 6.6 MVA. Determine the required minimum breaking capacity in kA. (Note: Covert 3-phase power in terms of kA to find answer.) b)Using the below, determine the required minimum making capacity in kA as a “peak value”. Rate breaking capacity (Icn) ka: Icn<= 1.5 Factor = 1.41 1.5
What is the difference between XLPE & FRLS cables? Is FRLS cables is a type of XLPE cable or both r different?
If you have an earth with pilecap then your resistance is really low. why and how?
what is the basic principle of TV camera?
What are the main parts of central chiller plant? Explain the function of each stage.
0 Answers HSL, Shankar Electricals,
How is the percentage impedence of a transformer fixed at design stage???
What is the rating of a circuit breaker needed for 300 kv load in 33KV supply line of 33/415 transformer ? Whether 800/1200 amp vaccum circuit breaker can perform for a 33 KV line in input in 415 volt in output of the transformer ?
why link is provided in neutral of an ac circuit and fuse in phase of ac circuit?