Answer / srinivasa rao talasila
VFD is designed to give a out put frequency of 1Hz to 600
Hz but our connected load has to with stand.
In our plant we are running the german motor name plate RPM
1775 at 60Hz but we are running the same at 87Hz RPM 2610.
In above case also bearing capacity to withstand such high
rpm and current of the motor should be with in the name
plate limits.
| Is This Answer Correct ? | 0 Yes | 0 No |
VFD can be vary upto 80hz but we need to set the limits
into parameter settings.
| Is This Answer Correct ? | 1 Yes | 2 No |
what is EIB lighting control system? what is the advantages of this system?
Neutral CT for 45MVA 132/11 KV YNd11 Transformer. NCT REF CLASS-PS or 5P20 with 20VA burden which is suitable.
PAC and simple Ac different
What is Ton Capacity of Air Conditioner?
how could we know the size of cable by physical view?
0 Answers Havells, United Engineering,
What is the formula of frequency ?
What are the causes of electrical faults?
If I want to buy a new Xformer for my plant what are the main parameter will I need to check?
what is the avr
6 Answers ArcelorMittal, Heidelberge Cement,
What is the main use of rotary phase converter ?
what is tesla ?
what is function and advantage of double delta winding in induction generator?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)