When capacitor bank connect on line. It's draw some current
but it's current not increase of main line ammeter. Why?
It is true only in case of a Load which is running a poor
power factor because capacitor draws the Leading current
which cancel outs the lagging current of load and thus no
current drawn from line but if a load which already having a
good power factor capacitor will draw the leading current
from the line.
For checking this fact, just switch on a capacitor on the
panel when there is no load condition.
Is This Answer Correct ? | 18 Yes | 1 No |
Using 11000V/433V,3 ph,50Hz,500 KVA, what is the maximum capacity of motor in KW that can be connected and started at a single moment? Also explain about any calculations and formulas used in deriving the same.
what is difference between power & distrubution transformer ?
In 11/0.414 KV Parralel supply network with Bus tie closed what will be the fault level is it doubled or halved??
how many types method in earth testing?
WHY RATING OF VCB NOT LESS THAN 630A
say a transformer is designed for 33/11kv step down with ratio 0.33 for load 1 mva. if am giving 11kv as a input that same transformer what will happen to its o/p voltage. and whether it can be operated for 500kva
High Voltage out door substation-annual maintenance, things to be considered
how can i improve the power factor in domestic (230v)
what's the reson that,Load is not same on VFD I/P and O/P Side.whenever DOL condition load is same I/P and O/P side.
What is short circuit analysis of electrical networks?What are the procedures to be followed for its calculation?
Slipring moter find external resistance
Why L.T.Cable voltage rating is 1.1kV,where as system voltage is 0.415kV?