will the turbogenerator operate on leading power factor
with out modification in the stator winding.
Answers were Sorted based on User's Feedback
Answer / s.k.mishra
yes,the turbogenerator will operate on leading power factor
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / hareesh
Turbogenerator is a synchronous generator and it can work in synchronous condenser mode also. When it is over excited, the generator will operate with leading powerfactor.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / kasa
tg can operate in leading p.f mode when it is under excited
condition but it is not advisable beczuse stator ends get
over heated due to leakage flux.
| Is This Answer Correct ? | 1 Yes | 3 No |
Explain why the Voltage drop will happen in 3 Phase line?
I have 2 KW electric water heater.I am gonna use it in controlling water temp.so I needed to increase or decrease the heating capacity.is there any electrical-electronic circuit for varying the resistance & so current?
How one can say about a device (e.g: a light holder contains 20 or 30 L.E.Ds which glows when power supply is off, from which source they are getting the supply..... battery or capacitor) without removing and opening up its case ?
If we connect a motor and generator together (I mean that the generator gives the motor electricity and the motor gives the generator movement) regardless the losses. Will the generator still generate and the motor still move?
how will you find out the fuse failure by remote operation?
why 3 phase induction motor only need starter ? why not other motors need starter ?(like synchronous motor,single phase induction motors & their types) ?
We have drive feeding an output contactor for a 5000 hp motor @ 5kV application. The motor FLA is 629amps x 1.25% service factor = 786.25 amps The cable that we current have in place between the drive and the output contactor is 350kcmil- MV-105 (parallel cables). Per the NEC table 310.60 (C) (69). This show the cable ampacity is at 615 amps per cable for a rating of 1230 amps. We have derated the cable for the cable tray and the multiple cables application and our calculations show that after the correction factor factor we are at 922amps. 1230 amps x .75% correction factor factor = 922.5 amps. The customer is driving us to then use another safety factor of .25% off of the already derated cable. Can you please provide a longhand calculation for your solution on this application?
please send the IS strandard for electrical to sakthi_murugan86@yahoo.co.in
How 3 phase invertor works?
Why cables and busbar both needed in LT Panels?
control wiring purpose,standards, ferrule code standard, interlock, schematic, symbol
what is the difference between capacitive voltage transformer & inductive voltage transformer.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)