what are the major & minor faults that occur in an inverter
and in UPS ? And how to repair and resolve them ?
No Answer is Posted For this Question
Be the First to Post Answer
what is V0/V rating of cable
What is duty cycle for HT motors? How many start permitted if mentioned as 01 for hot and 02 for cold per duty cycle?
how mass curve differs from hydrograph.
how can i change the rotation of the AC single phase induction motor and show me by diagram
Starting Time of LT & HT Motor
Lux meter is the measuring device to measure the lux level of lighting fixture. in industrial sector two types of lighting fixture is being used as street lighting purpose 1. HPSV (Sodium) and 2. HPMV (Mercury). HPMV having white light which is an combination of red, blue and yellow colour, while HPSV haivng Yellow lighting. in HPSV red & blue colour will be absent. during measurement of the lux level of HPSV and HPMV fixture. 1. Lux meter can measure the actual lux level of both fixture? 2. or it will show false reading for HPSV fixture light as it has only yellow light present. please give me answer
what is the form factor of DC voltage
What is pi controller?
Benifits of 3ph 4 wire metering over 3ph 3 wire
what is the main function of capacitors in mccs.
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
why three phase capacitor takes unbalanced current in capacitor bank?