what is the differance between normal bybass & maintenance
bybass in UPS?
Answer / ruben
UPS has internal bypass and used if in case there is some
problem within the UPS, ie. overload. the load will be
automatically fed from the bypass circuit. the maintenance
bypass is an external circuit or feeder that is use to feed
the load (bypassing the UPS). this will allow the user to
remove completely remove the UPS from the network/system for
maintenance or replacement.
Is This Answer Correct ? | 2 Yes | 0 No |