should I use Hydrostatic Pressure Transmitter for
measurement of DENSITY of filled tank ?
If YES then please explain how.
Answers were Sorted based on User's Feedback
Answer / raju b
yes you can use the liquid with density. you need to
workout the density calculation In E&H Txr this facility is
there
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / rajkumar
A fluid column generates a specific hydrostatic pressure as
a function of density and filling level. A pressure sensor
attached to the bottom of a tank measures this pressure with
respect to a reference pressure (generally ambient
pressure). Conclusions are then drawn as to the filling
level with the aid of the known fluid density. Hydrostatic
level measurement is suitable for virtually all types of
fluids and produces very precise measured values, dependent
on the accuracy of the pressure transmitter.
| Is This Answer Correct ? | 0 Yes | 2 No |
How to calibrate capillary type level transmitter
I have a orifice installed in plant which is design for 0~100 inH2O for 0~80MMSCFD, now due to process change the maximum flow is change to 120 MMSCFD so for this new process value what will be the DP across orifice.
how to calibrate transmitter
please any body have most important data for study for saudi aramco test of instrument QC thanks email shahnaveedullah@gmail.com
If a normal magnetic type flow transmitter that can measure flow, temperature and show this parameters on field, is it possible by any means to get this (flow and temperature) parameters info. On dcs? And if yes then with HART, FO communication or any other communication system?
1 Answers Process Control Technologies,
why magnetic flow meter is not used in thermel power plant operation
what is upstream and downstream in liquid flow?
Paper Details: company -- Hindustan Copper Limited post -- GET 2008 Date -- 03.08.2008 Dept.-- Electronics?Instrumentation Aptitude -- 70 Technical-- 80 Total Time -- 2hr 30min I have listed the question I could able to remember 1. BCD equivalent of 43 2. value of K for stability of a system from a given equation 3. transformer connection for darlington connection 4. damping of balastic galvanometer 5. advantage of chart-pen recorder over CRo 6. CRO - how to change bandwidth 7. questions on CRO construction 8. reverse saturation current of si diode 9. advantage of wire wound resistance over carbon resistance 10. core material for a small coil 11. max fanout-- TTL/ECL/CMOS/MOS 12. component of resistance of monolithic IC 13. functions of capacitors in multivibrators 14. to change a sawtooth signal into a square wave we use-- schmit trigger/ schottkey diode/ zener diode 15. relation b/w á & â in transistor ckt 16. function of SiO2 layer in fabrication 17. 3 questions on ODD MAN OUT
Can we measure pressure using differential pressure transmitter? If yes then how?
how to tune the closed pid loop?
how pressure reduce through pressure control valve? suppose we have to reduce 20 kg pressure to 10 kg pressure , then what we do ? open the valve or close the valve , initially it is 20 % is upon ( for ur knowledge ).
yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help me fine how we can normal the broblems?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)