how one can check the Current of a DC 12 V battery ?
Procedure.
I told that take a thick wire (having more wires in it) and
then join the + and - terminals of battery with the help of
two ends of a thick wire ....
is this correct or wrong .....
Answer / arun
It is not engineering practice!
You can have test lamps,meters to check it properly.
Is This Answer Correct ? | 3 Yes | 1 No |
what is the difference between rectifier and converter and commudator?
why power is generatd at 50 hz only..? can we do this on another freq...?
what efficiency of transformer at 100% load
a transformer can have zero voltage regulation a)o pf b)1 pf c)lagg pf d)lead pf
may anybody tell me the names of institute where plc programing course are conducted
One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?
what is the difference between LLL and LLLG fault ?
What is a thermocouple, and it working principle?
why DG rating in kva
What we change frequency from transformer. yes or no
Find the octal equivalent for the binary number 101101110
In my project i am layout cables under the Maintainance bay /Maintainance yard in the TG Building. Whether in this route i can lay the H.T.Cables??? i am taking all H.T cables from the H.T Transformer to the TG Building..