how to calculate the powerfactor in induction motor having
name plate details? for example 1 h.p motor 1.86 A 415 V
Answer Posted / md. zakir hosen
We know P=VICOSф.
Here, P=1H.P=746W,V=415v,I=1.85amp
Now putting this value on the equation simply we get the PF.
746=415*1.85*COSф
746
=>COSф=----------=0.9716 and it must be lagging.
415*1.85
More info: Earn and Learn pls visit
http://a2zengineering.blogspot.com/
| Is This Answer Correct ? | 18 Yes | 2 No |
Post New Answer View All Answers
what is the ckt diagram of a tubelight and is it the simplest ckt of electrical engineering and also the component?
wat is d diffr btw shunt coil and trip coil in VCB?
Inverter. converter. Ups.MCB.solar.alternators. motors.
What is a compensator?
Do you need any help with FEWA Electrical Supervisor exams?
What is nichols chart?
If ROC does not lies inside unit circle,then ? a) Fourier transform converges b) Z transform converges c) Hatly transform converges d) Colpit Transform converges.
10 tube light connect in mcb breaker.one tube light is fault.so breaker is tribe.how fault is rectified.(using 3wire phase,earth,neutral)
if 12v battery get discharged for 2 months after if we put charge it will charge again?how much time it will take to charge?
If 100 KAV USP dedicated earth got disconnect / Cut. What will happen at load.
Draw the equivalent circuit of crystal oscillator?
How to calculate the current of Highpressure Mercury Vapour Lamp?what is the basis?whether we have to consider power factor or not?
How will polarity test of Dy5 Transformer ?
WHAT IS THE PARTIAL DISCHARGE TEST?
what is V.L.F. testing of power cable? do you know the voltage ratings, like for what rating and size of cable what rating of V.L.F. testing is used?