when motor taking high amp what happen.
Answers were Sorted based on User's Feedback
Answer / arockia doss
Reasons Behind :
1. Loose Connection
2. Three phase cut into two phase
3. Winding Failure
4. Mechanical Damage/Overlaod
5. Higher Voltage/Frequency
If its so ,Breaker should get trip. If not it will damage
the motor.
Is This Answer Correct ? | 17 Yes | 3 No |
Answer / pillay
that means the motor is finding it harder to maintain
the speed. it could be due to so many reasons as already said
by DASS and VENKAT.
What happens is if any of the motor protective devices dont
trigger the motor to stop than it will continue to run
until the windings give way due to overheat and finally insulation breakdown which is commonly known as burnt.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / venkatesh sk
moto should be terminal loose& connetion&load more &
frquency very&motor capacity low& voltage low
Is This Answer Correct ? | 7 Yes | 5 No |
Answer / gagan kumptar gua
when a motor take high current the wiring of the winding
will be burnt becouse H is proposnal to square of
current.it happens due to loose connection or over load and
change in frequency of voltage.
Is This Answer Correct ? | 1 Yes | 0 No |
Hi,iam a diploma in electrical engineering.rtd from indian air force in apr 2007.prsently working in reliance next link as a network maintenance engineer since 2007,can i get a job in motherson sumi.
0 Answers Motherson, Motherson Molds and Diecasting Ltd.,
What size cable is used for HT cable to the transformer of 630kVA, and the supply voltage is 11kV
in case of induction motor when overload condition or any short ckt. why stator winding burn not to be rotor winding
What are the advantages of using distance protection schemes as opposed to normal overcurrent/ earth fault protection on high voltage feeders.
what is the right method of laying cable tray if we are using EOT crane in shed, better is below or up
What is CRT (Contact Resistance Test) for Isolators or Dis- connector Switches? Why we performed it & whats the Testing procedure.
Why the voltage n frequency of the incoming generator is kept slightly higher than d grid voltage n frequency while synchronization ?
when a primary current injection test is required, it is accomplished by what?
The slip during plugging operation is given by= A 1-s B 2+s C 1+s D 2-s
how to calculate the mesh earth network resistance in such substation, is there any recommended resistance values with references , thanks!
Dear Respected sir how to test ABB REX521 protection relay by relay tester.
what is positive , negative & zero equivalent system resistance