How to select Main CB Rating for 187 KW Load?
Answers were Sorted based on User's Feedback
Answer / abdulsubur
Total load =187kw
p=root3*vicosphi
i=p/root3v*cosphi
we get aprorximately 400
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / ramaraj.g
Selecting main CB rating first.
187KW / votages LL
187000/400
467.5 amps this type current rating is not in market
so we will go to next rating 600 Amps
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / abdulsubur
P= Root3*vicosphi
calculate i from this equation apploximately
we can use 400A ircuit Breaker
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / rajendran
Apart from the nominal operating current we have to
consider the following factors also
1) Capacity of the source
2) Fault lvel of the system
3) Breaaking capacity of the breakeer required based on the
fault level obtained..
4) Space avilable
5) cost requirements
6) Method of controls in the breaker
7) Protection facilties avilable....
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / bala
Selecting main cb rating depends on the type of load if it
is combination of small loads (upto 10kw) 400amps mccb is
enough.
1. if it is one motor load. first we have consider what
type of starter we are going to use. in case of star delta
starter select 600amps mccb. in case of VFD and softstarter
400amps mccb is enough.
| Is This Answer Correct ? | 4 Yes | 3 No |
formula for incomer breaker size calculation of powerfactor correction unit
Why we are using only Dyn11 tranformer in distribution system but not using a Dyn1 in distributing system?why not and advantage and disadvantage in both
difference between crane drive and line drive.
why use phase displacement in transformer.and effect of phase displacement on transformer
What is the RMS Value. Please discribe in detail
Why material of brush is carbon in motors why not other material.
1 ph induction motor winding priniple and connection diagram?Similarly for 3 ph induction motor?Full description
In our plant we have installed new MCC with ELR and CBCT which is detecting some leakage current in the system but it leading to some confusion when to check that in which feeder which is drawing current we put off the whole panel itself but still CBCT detecting some leakage current so can anybody ans me , where i am going wrong or how to detect whether its actual leakage or CBCT malfunctioning.
1.Is there any difference between terminologies,HT-HV <- LV? 2.What is the highest transmission voltage level in india?
how to check a three phase induction motor by multimeter & megger?
how to use single phase supply for a three phase equipement.
When we giving the 3 phase supply to ups system how to coming netural?
0 Answers Juniper Networks, Tata Motors,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)