why use generator Earthing/Graunding.
Answers were Sorted based on User's Feedback
Answer / r.p.saini ,cfcl
For protection of generator(Protection of stator and rotor
winding during short circuit or any other electrical fault)
as well as for human sfety aspects generator is always
earthed/grounded by two earthings.
| Is This Answer Correct ? | 13 Yes | 0 No |
Answer / kishore
generator is a highly investment equipment which should be
protected from the faults conditions and sudden changes in
the load and increase in the voltage abruptly when earthing
is given if forms a closed loop the currents take grounded
direction
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / ruthie
Ideally, the neutral point of a 3 phase star connected
generator is zero. As a means of protection of the
generator (stator and rotor windings)the neutral point is
grounded in order that inbalance of voltage between the
phases due to faulty conditions will be sent to ground.This
is to avoid breakdown of stator or rotor windings
insulation, or even severe burn of windings.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / ............vamsi..........
generator is a very costly and very useful equipment so
which should protect from fault conditions.sudden changes in
the load and increase in the voltage abruptly when earthing
is given if forms a closed loop the currents take grounded
direction......
| Is This Answer Correct ? | 1 Yes | 0 No |
how does a current carrying conductor posess a magnetic field. what is the reason for the production of electro magnetic field around the conductor
how to calculate short circuit calculation of the transformer by usuing the percentage impedence? formula needed.
what does mean for "mah" for mobile batteries like 1500mah,1300mah??
how do i calc busbar size for a rated current?
IN 3 PHASE INDUCTION MOTORS SOMETIMES COPPER BARS ARE PLACED DEEP IN ROTOR WHY..?
What is hipot test procedure?
How can we measure the residual voltage in dc machines?
can we replace Dyn11 transformer to Yy0 transformer and what is the difference between the two type
in india single phase is 230v and three phase is 440v but in other countries single phase is 110v and three phase is 380v why..?
We have 750KVA DG set, we want to introduce REF relay with 1250/1A,CL PS,Current transformers.The lead distance of 2.5mm copper flexible cable from CT to relay is around 5mtrs.We would like to know the knee point votage(VK) & IM calculion for CT's
what will be the difference on output when 3phase I.M. is given a delta or star supply?
i have interview in Pepsi company what type of question will ask please send the question and answeer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)