why use generator Earthing/Graunding.
Answers were Sorted based on User's Feedback
Answer / r.p.saini ,cfcl
For protection of generator(Protection of stator and rotor
winding during short circuit or any other electrical fault)
as well as for human sfety aspects generator is always
earthed/grounded by two earthings.
| Is This Answer Correct ? | 13 Yes | 0 No |
Answer / kishore
generator is a highly investment equipment which should be
protected from the faults conditions and sudden changes in
the load and increase in the voltage abruptly when earthing
is given if forms a closed loop the currents take grounded
direction
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / ruthie
Ideally, the neutral point of a 3 phase star connected
generator is zero. As a means of protection of the
generator (stator and rotor windings)the neutral point is
grounded in order that inbalance of voltage between the
phases due to faulty conditions will be sent to ground.This
is to avoid breakdown of stator or rotor windings
insulation, or even severe burn of windings.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / ............vamsi..........
generator is a very costly and very useful equipment so
which should protect from fault conditions.sudden changes in
the load and increase in the voltage abruptly when earthing
is given if forms a closed loop the currents take grounded
direction......
| Is This Answer Correct ? | 1 Yes | 0 No |
how do you test the capacitor bank ?
what is EBXl (electron beam cross linked ) cable ?
Is there any specialised book to refer about fault level calculation both in MV and LV side??
We've 2 diffrent DG's with same capacity (500 KVA). Can we sync them ?
Kindly Tell me name of the book for electrical estimation and costing ,calculation or web site to download
what shoud be strength and weakness to impress interviewer????????
why t/f are rated in kva. is it conserned with p.f.
In an electrical power supply,why if neutral phase of a 3phase supply fail over current occur but if it's single phase supply neutral phase fail low current occur?
If two transformers same rating(11KV / 440V)connected in the same primary line(11KV), can we connect(bus coupler) secondary side directly or need a synchronization????
what is the meaning of "i.p.-43" and duty cycle-s1 on the name plate of a asynchronous machine?
why CT output is always raetd 5.regardsof primery curre.
1.what is use of isolation transformer. 2.Differance between KWH,KVAH,KVARH,KVA. 3.Main use of the CT and PT.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)