Answer / rajesh t k
The NAT and NAC contacts are provided on TNC switch to facilitate additional functionalities from the TNC switch than mere Tripping or Closing.
These contacts are also known as Lost Motion Contacts. They help identify the last operation (Trip/Close) performed by the operator through the TNC switch.
The NAC contact will be closed whenever the operator turns the TNC lever to Close position and the contacts stays closed even after the lever is returned to the Neutral position by the operator, until the lever is turned to Trip side.
Hence, the 'Auto Trip' indication can be given via the NAC contact(instead of giving through an NO contact of the master trip relay), in series with the CB's 52b contact. That is, this is just an alternate way to wire up the 'Auto Trip' indication.
The NAT contact, likewise will be through whenever the CB has tripped via the TNC lever switch by the operator, until the lever is turned to Close position again.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / k.prakashchandra
NAT- normal after trip and NAC normal after close.These are
'lost motion contacts' which indicate last operated position
of breaker .With NAC contact we get 'Auto-trip' indication
when the breaker is tripped by relay.
| Is This Answer Correct ? | 12 Yes | 5 No |
What is the importance of creepage distance in disc insulator ?
Why dnt we generate 5-ph or 7-ph supply like as 3-ph supply
How check proper electrical earthing of machine.
What is the use of Isolation Transformer, and Neutral is using for return path, finally this current is going.... but same time the voltage of the neutral should be below 1 V...
if we use fuse in neutral what will happen?
DEAR SIR/MADAM,CLEARLY EXPLAIN ABOUT CRAWLING AND COGGING EFFECTS IN INDUCTION MOTOR.
what is the reqirred voltage in HT motor to get full RPM on no load test?
What is EOL?
During Starter Panel Com missing I Found The Main Incomer 40Amp MCB 10KA Trip When Motor Change Star To Delta Motor Rating 20HP BUT When We Use Same MCB To Other Motor It Does Not trip Or What Is Necessaries for Star Delta Starter MCB SFU MPCB OR MCCB And What are The Breaking Capacity of MCCB in the Motor above 15HP
what is the difference between directional & non directional earth fault with example please explain.
i need project topics along with circuit diagram in the electrical and electronics engg and also some websites regarding projets.
does over charging of a battery reduce its life?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)