Answer / rajesh t k
The NAT and NAC contacts are provided on TNC switch to facilitate additional functionalities from the TNC switch than mere Tripping or Closing.
These contacts are also known as Lost Motion Contacts. They help identify the last operation (Trip/Close) performed by the operator through the TNC switch.
The NAC contact will be closed whenever the operator turns the TNC lever to Close position and the contacts stays closed even after the lever is returned to the Neutral position by the operator, until the lever is turned to Trip side.
Hence, the 'Auto Trip' indication can be given via the NAC contact(instead of giving through an NO contact of the master trip relay), in series with the CB's 52b contact. That is, this is just an alternate way to wire up the 'Auto Trip' indication.
The NAT contact, likewise will be through whenever the CB has tripped via the TNC lever switch by the operator, until the lever is turned to Close position again.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / k.prakashchandra
NAT- normal after trip and NAC normal after close.These are
'lost motion contacts' which indicate last operated position
of breaker .With NAC contact we get 'Auto-trip' indication
when the breaker is tripped by relay.
| Is This Answer Correct ? | 12 Yes | 5 No |
why occ curve is not tracing back when we are bringing rheostat back in reverse direction?
what is the different ratings of ACB/VCB/SF6 which is used at HT side
Frequency in the control system represents? Continuous system in time domain ? In frequency domain?
how we calculate the withstansing current capacity of wires&cables?
what is lumped and distributed elements?
What do you mean by a phase angel of instrument transformer?
what is difference between 9kv 5ka surge arrester and 9kv 10ka surge arrester.
I know current,volt,powerfactor of an electrical line. In this line how I will calculate Active power and Reactive power
Whar is the KvA rating of 33Kv substation & actual kv rating of power generaating station.
I have 2 transformers in two different plants, both are without OLTC but i am facing problem of voltage fluctuation at LV side from only one transformer. i have to change its taps manually twice in a day. Another transformer delivering voltage is ok. Please guide me about the problem
Hi If connecting a temp generator 670KVA .415kv with step up Tx .415/11kv. I am given Generator impedances Z1 Z2 Z0 to 100MVA base. Do I need to work out the generator fault current by using these impedances i.e gen rating / impedance. Then use this as my source impedance for the calculations that follow.
What is The function of tvm(tri-vector meter)??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)