1.generator rated as 1000 mva,11kv .8 pf what will 0.8 pf
will indicate?
1.max pf it can supply 2.min pf it can supply
like this 4 options there what is answer.explain
Answers were Sorted based on User's Feedback
the above mentioned genrator Ans is 1.
it can supply max. load i.e 0.8 pf means 80 percent of rated
1000*0.8=8MW.
| Is This Answer Correct ? | 11 Yes | 2 No |
i agree with Mr Reddy.
Generator rated at 1000MVA at 0.8 pf 11Kv
In terms of KW the prime mover had been designed for this Gen is 1000 MVA X 0.8 = 800kw, any thing more can destroy your prime mover in the long run
now the alternator part is 1000 MVA AT 11KV
The max amps it can carry is 1000000/1.732/11000= 52.5A /phase
now you can operate the generator at any pf you want as long as you do not exceed 52.5 amps per phase.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / sreenivasalareddy
I will deliver (generator design)800mw power wether it
running at .8 PF or unity pf
When Generator runnig at upf we should alert we should not
load alternator to its rated current
Because your out put power will become 120 % almost ,Which
is not design for this load (Primover)
As for as my concerned pf is restrited to protect promover
and alternater eigher way
| Is This Answer Correct ? | 5 Yes | 2 No |
Why r u using pf panel. what the uses
What is the megger value for ht
Why do we mix soda with water in LRS?
Frequency of rotor emf in induction motor is around A same as stator frequency B 50% C 5 % or below D 30%
When placed close together, two positively charged materials will
what is the relationship between current and frequency in AC circuit?
A 1F capacitor is charged to 100V initially. A 1H inductor is connected accros the capacitor througha a switch. The current in the circiut when the switch is closed is____
will a bulb glow connected to two phases of a delta connection?
How can I calculate the fault level of a transformer. 1. If fault is 3phase fault 2. If fault is 1phase fault 3. If fault is 2phase fault Dear all geniouses, can you help me by giving answer. If anybody want to send something then mail me at "msalam_shahin@yahoo.com"
what is tha between elcb & rccb?
surge tank, hrc fuse, earthing transformer, firm power objective type
What is the maximun current carring capacity in per phase for three pole 100anps rating ncb
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)