Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


formula for cable size calculation for current?

Answers were Sorted based on User's Feedback



formula for cable size calculation for current?..

Answer / govardhana rao.p

Calculations are same as above but for 50A load

We can use the bellow cables

Aluminium: 50 x 3.5 Core

Cu : 16 x 4 Core

Is This Answer Correct ?    115 Yes 61 No

formula for cable size calculation for current?..

Answer / sabu

in case 50amps 230v single phase load we can use 16mm aluminium and 10mm copper

Is This Answer Correct ?    29 Yes 6 No

formula for cable size calculation for current?..

Answer / zafar

the answer is not correct the correct figure is 25mmsq

Is This Answer Correct ?    37 Yes 19 No

formula for cable size calculation for current?..

Answer / bipin naik

The current will be 27 A for single phase supply(230v)

Is This Answer Correct ?    4 Yes 0 No

formula for cable size calculation for current?..

Answer / fathi

2x10 sqmm Cu/XLPE/PVC 600/1000 v

Is This Answer Correct ?    17 Yes 16 No

formula for cable size calculation for current?..

Answer / engr.muhammad younas khan

SINGLE PHASE FORMULA FOR CABLE SIZING.

REQUIRED DATA:-
I :- AMPERES
L :- LENGTH OF CABLE.
K :- CONDUCTIVITY OF COPPER(58)
:- CONDUCTIVITY OF ALUMINUM (36)
Vd:- VOLTAGE DROP.

GIVEN DATA:
I:- 50 AMPERES.
L:- 100 METERS.
Vd:- 3% ACCEPTABLE OF 230 VOLTS

FORMULA:-
AREA (mm2)= 2*I*L/(K*Vd)
= 2*50*100/(58*6.9)
= 24.98 mm2
= ALMOST 25 mm2
FOR THREE PHASE:
AREA(mm2) = 1.732*50*100/(58*12)
= 12.44 mm2
= ALMOST 15 mm2
3% voltage drop of 400 volts =12 volts.

ABOVE EXPLAINED FOR IS PROPERLT CORRECT.USE AND ENJOY.

ENGR.MUHAMMAD YOUNAS KHAN
M.SC.ENGG.MIEE(UK)
WAZIRABAD CITY,PUNJAB, PAKISTAN
DATE:- 24/3/2014

Is This Answer Correct ?    2 Yes 2 No

formula for cable size calculation for current?..

Answer / selvakumar

230 meter cable

Is This Answer Correct ?    2 Yes 3 No

formula for cable size calculation for current?..

Answer / lorp soophan

S=(2.l.i.cosg)/V%

Is This Answer Correct ?    0 Yes 4 No

formula for cable size calculation for current?..

Answer / vinay katoch

formula is same but for 50 amp load we can use 3.5c
25mmseq.all.and 10mm seq.cu.

Is This Answer Correct ?    18 Yes 28 No

formula for cable size calculation for current?..

Answer / gurunadharaov

by the formula p=v*i*cos@
assume the load as 5kw and operating at 230v and also
assume the load as inductive (so the power factor is 0.5
pf lag)


now by formula
5000=230*i*0.5
i=50A
NOW CABLE SIZE MUST BE > LOAD
SO CABLE SIZE IZ 65SQMM(ITZ DSSEPEND ON AL/CU CABLE)

Is This Answer Correct ?    118 Yes 136 No

Post New Answer

More Electrical Engineering Interview Questions

As we know induction squirrel cage motor torque Directly praprortinal to applied voltage in star connection & delta also. If I connect 55KW Motor to DOL starter in load condition does motor withstand the load & what will be the current withdrawn ? motor will not fail ?

0 Answers  


1.what is the difference between ct and cvt? 2.what is the difference between pt and cvt? 3.what is the difference between relays and circuit breakers?

0 Answers  


what is wore of PLC ?

1 Answers  


in thermal overload relay class 10A indicate what

6 Answers   Reliance,


Can I Drain A Oil For Sample When The Transformer is Running? (Charged)

2 Answers  


ther is any difference if we use 240 V A.C,50 Hz,1 Ph. in place of 230 V A.C,50 Hz,1 Ph.

4 Answers  


Brushless excitation of synchronous generators and motors

2 Answers   AMIE,


testing of Vector Group – YNaoD II

0 Answers  


The formular of how to calculate a cross sectional cable to feed an electric motor. Examle: 15KW, 26.1A, 415V. Calculate the cable size in mm2

3 Answers   Sona,


What is the Derating factor of power cables when exposed to direct sunlight in (both PVC & XLPE).

1 Answers  


why the generating / transmitting voltage is in the order of multiples of 11(ie 11kv,22kv,33kv......)

1 Answers  


For 280kw power. Which cable I can usr

3 Answers   Clean World, TCS,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)