formula for cable size calculation for current?
Answers were Sorted based on User's Feedback
Answer / govardhana rao.p
Calculations are same as above but for 50A load
We can use the bellow cables
Aluminium: 50 x 3.5 Core
Cu : 16 x 4 Core
| Is This Answer Correct ? | 115 Yes | 61 No |
Answer / sabu
in case 50amps 230v single phase load we can use 16mm aluminium and 10mm copper
| Is This Answer Correct ? | 29 Yes | 6 No |
Answer / zafar
the answer is not correct the correct figure is 25mmsq
| Is This Answer Correct ? | 37 Yes | 19 No |
Answer / bipin naik
The current will be 27 A for single phase supply(230v)
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / engr.muhammad younas khan
SINGLE PHASE FORMULA FOR CABLE SIZING.
REQUIRED DATA:-
I :- AMPERES
L :- LENGTH OF CABLE.
K :- CONDUCTIVITY OF COPPER(58)
:- CONDUCTIVITY OF ALUMINUM (36)
Vd:- VOLTAGE DROP.
GIVEN DATA:
I:- 50 AMPERES.
L:- 100 METERS.
Vd:- 3% ACCEPTABLE OF 230 VOLTS
FORMULA:-
AREA (mm2)= 2*I*L/(K*Vd)
= 2*50*100/(58*6.9)
= 24.98 mm2
= ALMOST 25 mm2
FOR THREE PHASE:
AREA(mm2) = 1.732*50*100/(58*12)
= 12.44 mm2
= ALMOST 15 mm2
3% voltage drop of 400 volts =12 volts.
ABOVE EXPLAINED FOR IS PROPERLT CORRECT.USE AND ENJOY.
ENGR.MUHAMMAD YOUNAS KHAN
M.SC.ENGG.MIEE(UK)
WAZIRABAD CITY,PUNJAB, PAKISTAN
DATE:- 24/3/2014
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / vinay katoch
formula is same but for 50 amp load we can use 3.5c
25mmseq.all.and 10mm seq.cu.
| Is This Answer Correct ? | 18 Yes | 28 No |
Answer / gurunadharaov
by the formula p=v*i*cos@
assume the load as 5kw and operating at 230v and also
assume the load as inductive (so the power factor is 0.5
pf lag)
now by formula
5000=230*i*0.5
i=50A
NOW CABLE SIZE MUST BE > LOAD
SO CABLE SIZE IZ 65SQMM(ITZ DSSEPEND ON AL/CU CABLE)
| Is This Answer Correct ? | 118 Yes | 136 No |
Can a dc motor works as a dc generator. If yes , then how?
what is the voltage between the earth & neutral 2 is there any continuity TO BE between earth & NEUTRAL
What will happen when a DC series motor suppllied by an AC source ?
what principle the cabel TV channels are transmitted? will you be able to check the power at the connector behind your TV with a tester?If yes what is the supply level?
Pls say , how we calculate lux / sq.ft, which formula used for calculation
Three phase star connected PT transformer primary side one phase fuse is blown what will be the output in secondary side(Secondary side also three phase star connected)
If we have two nodes A and B and Vab is the potential difference between these nodes then which node is called reference node a.node A b.node B c. Ground node
What are the causes of electrical faults?
How to calcluate the current by means wires/cables in square mm
sir my exam is on 19/6/2013 under electrical branch pls send me sample aptitude questions as well as sample technical questions for jindal steel and power company
whether a separate starter is used for a motor while it is connected to a vvvf panel?
how many earthing should give for transformer body and nuetral
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)