how to calculate the current if i know power in MW and
voltage 11kv/415v and also want to know that incoming
cables for trnsformer
Answers were Sorted based on User's Feedback
Answer / sripellirajukumar
hi this is rajkumar...
as per my knowledge
the primary side current can be calculate as follows
for example
we have power transformer of 5MW transformer and the 33\11kv
the primary current is (5000kv/33kv)/1.732=87.47amps
the secondary current is (5000kv/11kv)/1.732=262.43amps
here 1.732 is square root of 3....
| Is This Answer Correct ? | 43 Yes | 18 No |
Answer / cfanez
Girish,since the power is in MW,it means that we are looking
for current in consideration of power factor.If it were in
MVA,then the calculation given by Rajkumar is ideal.
5000kW=1.732*11*Ip*PF (assume pf =0.85)
5000=1.732*11*Ip*0.85
primary current Ip=308.7A
5000=1.732*.415*Is*0.85
Secondary currentIs=8,183.6A
Select cable capable from your table.If surface then
alluminum cable should be selected,if underground,suitable
hV cable should be selected to suit the primary and
secondary current carrying capacities respectively.
| Is This Answer Correct ? | 15 Yes | 6 No |
Answer / tasawar abbas
power factor panel calculation?
why I use the PFI panel in industry?
whose I select the kvar rating?
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / j.kesavan
check tr current in name plate py side after slect h.t
(xlpe)cable fix .
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / hosam
33000KV/11000KV 20MVA = 20000KVAX0.8=16000KW
1000kva H.V=52.5
L.V=1333.4
433V
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / perumalsamy o
5mva
I = 5000/33*1.732
I = 57.5A (HT amps 33 kv side)
I = 5000/11*1.732
=262.5A(HT amps 11kv side)
| Is This Answer Correct ? | 1 Yes | 9 No |
What difference between voltage and current
what is the merz prodution ? what is the turn to turn fault?
what is S.T?specify the range?
What is the need for checking knee point voltage for CT's?
I want to know what must the CT ratio be on a load of 300A is a 3PH nutral to earh installation?
A power transformer 4MVA/11KV/0.415Kv has been out of use in 12years. what maintenance actions/test need to be carried out before energizing.
Why the transformers are rating in KVA.?
when we have to use UPF wattmeter and LPF wattmeter? what is the difference between UPF and LPF wattmeter in terms of construction?
why generator one end side star neutral point given? if this point not given what happen?
How will you define capacitance?
Is earthing done for AC or DC or both?
a 3 phase motor was running with delta connected, suddenly one phase winding got burnt off, what will be the effect ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)