Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to calculate the current if i know power in MW and
voltage 11kv/415v and also want to know that incoming
cables for trnsformer

Answers were Sorted based on User's Feedback



how to calculate the current if i know power in MW and voltage 11kv/415v and also want to know tha..

Answer / sripellirajukumar

hi this is rajkumar...
as per my knowledge
the primary side current can be calculate as follows
for example
we have power transformer of 5MW transformer and the 33\11kv
the primary current is (5000kv/33kv)/1.732=87.47amps
the secondary current is (5000kv/11kv)/1.732=262.43amps
here 1.732 is square root of 3....

Is This Answer Correct ?    43 Yes 18 No

how to calculate the current if i know power in MW and voltage 11kv/415v and also want to know tha..

Answer / cfanez

Girish,since the power is in MW,it means that we are looking
for current in consideration of power factor.If it were in
MVA,then the calculation given by Rajkumar is ideal.
5000kW=1.732*11*Ip*PF (assume pf =0.85)
5000=1.732*11*Ip*0.85
primary current Ip=308.7A
5000=1.732*.415*Is*0.85
Secondary currentIs=8,183.6A
Select cable capable from your table.If surface then
alluminum cable should be selected,if underground,suitable
hV cable should be selected to suit the primary and
secondary current carrying capacities respectively.

Is This Answer Correct ?    15 Yes 6 No

how to calculate the current if i know power in MW and voltage 11kv/415v and also want to know tha..

Answer / tasawar abbas

power factor panel calculation?
why I use the PFI panel in industry?
whose I select the kvar rating?

Is This Answer Correct ?    6 Yes 4 No

how to calculate the current if i know power in MW and voltage 11kv/415v and also want to know tha..

Answer / j.kesavan

check tr current in name plate py side after slect h.t
(xlpe)cable fix .

Is This Answer Correct ?    2 Yes 2 No

how to calculate the current if i know power in MW and voltage 11kv/415v and also want to know tha..

Answer / hosam

33000KV/11000KV 20MVA = 20000KVAX0.8=16000KW

1000kva H.V=52.5
L.V=1333.4
433V

Is This Answer Correct ?    2 Yes 2 No

how to calculate the current if i know power in MW and voltage 11kv/415v and also want to know tha..

Answer / perumalsamy o

5mva
I = 5000/33*1.732
I = 57.5A (HT amps 33 kv side)
 I = 5000/11*1.732
   =262.5A(HT amps 11kv side)

Is This Answer Correct ?    1 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

which is more dangerous A.c or D.C?

26 Answers  


The efficiency of a 100kva transformer is 0.98 at full load as well as half load , for this transformer what is the Copper loss at full load ?

0 Answers  


We have one 500KVA transformer. We have tested REF relay and commissioned. After one and half year, due to some ground fault in one of the DB circuit Transformer tripped by REF relay. What will be cause and remedy. Please advise?

1 Answers  


does the transmission line model also requier active power in no-load operation?

1 Answers  


what is the diffrance between earthing and grounding...?

6 Answers   Essar,


what is the impedance voltage of transformer?

1 Answers   AVI Enterprises, MacLellan,


the input mechanical power of a single alternator is increased,its RPM increased but in case of an alternator synchronised with grid its RPM does not increased with increase of input mechanical power. why?

3 Answers   Bhel,


why reactive power control is required

5 Answers  


how on load transformer is chnage the Tapping ?

2 Answers  


3phase motor 400v (induction) A.C 4kw company design 1400rpm but our requirement 2000rpm possible? attached any instrument. reply fast! contact 03343262442

3 Answers  


What is the name of transformer oil?

18 Answers  


why electrical power has benn needed for speed controller of woodward governor control for biomas power plant

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)