Answer / sripellirajukumar
hi this is rajkumar...
as per my knowledge
the primary side current can be calculate as follows
for example
we have power transformer of 5MW transformer and the 33\11kv
the primary current is (5000kv/33kv)/1.732=87.47amps
the secondary current is (5000kv/11kv)/1.732=262.43amps
here 1.732 is square root of 3....
| Is This Answer Correct ? | 43 Yes | 18 No |
Answer / cfanez
Girish,since the power is in MW,it means that we are looking
for current in consideration of power factor.If it were in
MVA,then the calculation given by Rajkumar is ideal.
5000kW=1.732*11*Ip*PF (assume pf =0.85)
5000=1.732*11*Ip*0.85
primary current Ip=308.7A
5000=1.732*.415*Is*0.85
Secondary currentIs=8,183.6A
Select cable capable from your table.If surface then
alluminum cable should be selected,if underground,suitable
hV cable should be selected to suit the primary and
secondary current carrying capacities respectively.
| Is This Answer Correct ? | 15 Yes | 6 No |
Answer / tasawar abbas
power factor panel calculation?
why I use the PFI panel in industry?
whose I select the kvar rating?
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / j.kesavan
check tr current in name plate py side after slect h.t
(xlpe)cable fix .
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / hosam
33000KV/11000KV 20MVA = 20000KVAX0.8=16000KW
1000kva H.V=52.5
L.V=1333.4
433V
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / perumalsamy o
5mva
I = 5000/33*1.732
I = 57.5A (HT amps 33 kv side)
I = 5000/11*1.732
=262.5A(HT amps 11kv side)
| Is This Answer Correct ? | 1 Yes | 9 No |
what is tpmo switch
explain the functions of main isolation switches
what is the difference between cable routing and scheduling?
Why we are using air gap magnetic condutors
a bulb of 100W and anather bulb of 200W , rated supply voltage 230v.when supply voltage is reduced to 100v,which bulb will give more light? and why with calculation?
whats the advantage and disadvantage in TUMETIC mdel transformer
2 v/500amp/hr to 1.80vpc at 20 degree celsious 2v/5ooamp/hr to 1.75 vpc at 77degree farren .this is the capacity of a battery .what is the meaning of this . can i get a detailed explenation
why we earth only one side of a power cable. And which side is advisable to earth.
fuses rated by amperes but not power,why?
can we use ac ameter as dc ameter with ct
what is the Maximum voltage range for single phase
what is international rules of electrical?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)