how to calculate the current if i know power in MW and
voltage 11kv/415v and also want to know that incoming
cables for trnsformer
Answers were Sorted based on User's Feedback
Answer / sripellirajukumar
hi this is rajkumar...
as per my knowledge
the primary side current can be calculate as follows
for example
we have power transformer of 5MW transformer and the 33\11kv
the primary current is (5000kv/33kv)/1.732=87.47amps
the secondary current is (5000kv/11kv)/1.732=262.43amps
here 1.732 is square root of 3....
Is This Answer Correct ? | 43 Yes | 18 No |
Answer / cfanez
Girish,since the power is in MW,it means that we are looking
for current in consideration of power factor.If it were in
MVA,then the calculation given by Rajkumar is ideal.
5000kW=1.732*11*Ip*PF (assume pf =0.85)
5000=1.732*11*Ip*0.85
primary current Ip=308.7A
5000=1.732*.415*Is*0.85
Secondary currentIs=8,183.6A
Select cable capable from your table.If surface then
alluminum cable should be selected,if underground,suitable
hV cable should be selected to suit the primary and
secondary current carrying capacities respectively.
Is This Answer Correct ? | 15 Yes | 6 No |
Answer / tasawar abbas
power factor panel calculation?
why I use the PFI panel in industry?
whose I select the kvar rating?
Is This Answer Correct ? | 6 Yes | 4 No |
Answer / j.kesavan
check tr current in name plate py side after slect h.t
(xlpe)cable fix .
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / hosam
33000KV/11000KV 20MVA = 20000KVAX0.8=16000KW
1000kva H.V=52.5
L.V=1333.4
433V
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / perumalsamy o
5mva
I = 5000/33*1.732
I = 57.5A (HT amps 33 kv side)
I = 5000/11*1.732
=262.5A(HT amps 11kv side)
Is This Answer Correct ? | 1 Yes | 9 No |
what is the difference between energy efficient and high efficiency motors
how can i get elcctrical supervisor license & Certificate of competancy in gujarat? i have completed my B.E (Electrical) course from gujarat.
how to reduce earth resistance in sandy soil.
How to do fabrication , busbar and wiring cost for : 1. LT Panels 2. C& R Panel
A 3PH MOTOR RUNNING IN NORMAL CONDITION AND ITS AMPERE ALSO UNDER ITS FULL LOAD CURRENT,ITS CABLE RATINGS ALSO HIGER THN ITS CAPACITY,BUT ITS CABLE GETTING ABNORMAL HEAT(NOT TOO HOT)WHY ITS GETTING HOT LIK THIS
what is meant by k-rating in isolation transformer?what is k9, k14 stands for?
please let me know , we have installed two separate motor for fire fighting system 1) 60 hp and 2) 15 hp the load is 74 AMPS and 20 AMPS then tell me the main power cable in Aluminum will be what thickness , the length is 225 mt from the main utility to fire pump house
what is NGR in generator?
can indirect loading be called as phantom loading?
what is high voltage in india?
why does a dc machine has high efficiency while working as a generator than as a motor ..
what is the differance between ac induction motor and ac synchronous motor?