Answer / shailender gupta
Ans is right but required
calculation.is
p= root(3) VI COS phi.
find out current i.e I after
putting the value of V , p cosphi
and you will get required
current and multiply with 1.75
acc. to IEC fir safty purpose for
equipment
Is This Answer Correct ? | 3 Yes | 0 No |
ACB generally refers to Air Circuit Breaker used for the protection of devices from overloadings or short circuit currents has its range upto 1600A.
MCCB generally refers to Moulded Case Circuit Breaker has its range from 15A to 1600 and generally start at 14kAIC but go up to 100kAIC for applications with high fault current capacity.
So essentially, an ACB is used as almost the last line of defense during a fault. ACB are designed to be field maintainable, unlike MCCBs which are not.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / e.r k.k dash
Suppose there is 750 kva transformer.then acb can choosen by following foamula=kva*1.35=amp
750*1.35=1012.50 amp
So next higher range is chossen.that is 1250 4 pole with high breaking capacity.
Is This Answer Correct ? | 1 Yes | 1 No |
what is the difference between ACTIVE POWER and REACTIVE POWER.I WANT CLEAR ANSEWER.
What are the advantages of DOL starter?
what are different types of excitation in synchronous generator,what is the difference between them
what is impedence voltage
What are applications of Shunt release?
2 Answers Techno Electric and Engineering,
Wat is meant by OLTC?
What is the major difference between cnc and plc. why cant we use plc instead of cnc
Why carbon brushes are used in motors?
difference between moore and mealy model
Mechanism of Wye Delta Starter?
what is the safe meggar values for motor, transformer HT, LT and Cables? IF we want to replace I/C bay at our 220 kv substation which is of 140 mw load capacity bay to be replaced by 400 mw capacity bay.other than CT(1200/1) what are the other equipment i have to replace. why we generally use 3.5 core cable or in other word 1/2 core for neutral and also confirm me that in balance conditiob(3 phase)current in neutral will zero
How you will determine the volume of oil in a particular Distribution transformer.