Why Neutral Earthing pits and body earthing is
interconnected
Answers were Sorted based on User's Feedback
Answer / kaustav bhadury
Body earth pits and Neutral earth pits must never be
interconnected.
As per Indian Standards, they must be seperately grounded
into different Earth pits.
| Is This Answer Correct ? | 15 Yes | 2 No |
Answer / dayal varma
to make standby if neutral fail then the device get the
neutral from the earthing.
| Is This Answer Correct ? | 10 Yes | 10 No |
Answer / yogesh
If neutral earthing pit is separate & body earthing is
separate & if there is body earth fault voltage will develop
at the body suppose 230 V & someone touches body & neutral
potential difference will be 230 V & person will get shock.
If both pits are interconnected same potential will be there
& PD will be zero. So no shock.
| Is This Answer Correct ? | 2 Yes | 6 No |
What is the formula to calculate the rating of a thermal over load relay
Tell me about Simence PLC 'BLOCK'.How many types and what for.
Will an earth leakage trip be activated if the component or wiring is faulty on low voltage equipment.Example An electrical Cat Scarer placed in the garden and water gets into the wiring.
How to design the no. of ceiling fans required in 5mtr X 10 mtr X 3 Mtr hight room?
HOW DO A DISTANCE RELAY SENSES THE FAULTY ZONE.
what are the differance between neutral and earthing?
what is pure resistive circuit and pure inductive circuit
which of the following elements is not present in stainless steel
what is meant by residual over voltage & residual earth fault ?
On which side, taps are provided in tap changing transformers and why?
why DC motor body is plain cover but AC motor is different like finse?
there is a power transformer 66/11kV in delta-delta connection has 5 feeder coming out from the secondary side. One of the feeder in it normally loaded (loaded than other feeder)and this feeder usually trips with double OCR causing the bank transformer to trip. Now if the load of this feeder is put on other transformer then that no problems occurs on that transformer or the load. However normally all the test(IR, PI, short ckt, open ckt,grounding test and other ) has been conducted for this but evertything transformer..... I am not geting what is the actual problem...
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)