what is the difference between between open delta and
broken delta?
Answers were Sorted based on User's Feedback
Answer / kc
An open delta is 2 transformers connected in delta. It is
used to get three phase power using 2 transformers.
A broken delta is 3 transformers connected in delta, but
not closing the delta. The voltage across the open corner
of the delta is used for voltage polarizing or ground
detection.
| Is This Answer Correct ? | 56 Yes | 4 No |
Answer / engineer tanweer hussain
in delta delta connection no difficulty faced against 3rd harmonic because path for circulating current is avoidable. Operating advantage in delta delta is that when one unit is removed from service the remaining can be operated in open open delta at reduced loading of 57% and not 2/3 of full capacity .
Proof.
Power in V/power in closed delta = (3)1/3 Vph Iph/3Vph Ih
= 1/1.732*100= 57.7%
| Is This Answer Correct ? | 4 Yes | 0 No |
in open delta between there is no follow of current
But in broken delta 57 % load current folow between two
phases ...............
| Is This Answer Correct ? | 12 Yes | 28 No |
Answer / dayal varma
broken have some continuty open doesn't have any continuity
| Is This Answer Correct ? | 4 Yes | 42 No |
why diesel tank is earthed
a transformer can beb used as aload?give discription
2 Answers Esses Eltech Systems,
How to Calculate Transformer Earthing Electrode Rod Size both Body and neutral Earthing ? Any Standard Formula? Please Suggted
Classify driling machines.
which of the folowing has negative temperature coefficient of resistance? a. mercury b. copper c. lead d. carbon
750kva 11/415kv transformer having percentage impedence is5.64%. 11KV HV whose current 39.37A and 415V LV whose current 1043.43A.resistance is 2.5ohm. find no load loss and full load loss?
2 electric bulbs of 100w,200V are put in series & the combination of each bulb is supplied to 100 V . the power consumption of each bulb will be????????
i have 28/32 MVA power transformer with 11/6.6 KC voltage rating and 12%impedance.it have star connection at both side.but it have another thied winding tertiary winding.what is used of this winding. pl tell me
why a pure inductive circuit has zero power output?
is that any software calculator to calculate the size of cable
DG B-check,C-Check,D-check is depending upon the running hrs.If the running hrs is not reached as mentioned.How to conduct the DG checks.
The advantages of Magnetic flux leakage technique over Ultrasonic technique for non distructive testing of material.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)