How Calculat the Cable Sizing of HT/LT System & Explian by
one Exampal?
Answer / habib
Cable size (sq.mm.) is selected dpendent on 4 facors
1. Current carrying capacity (popularly termed Amapcity)
of the cable.
2. Voltage drop that can be tolerated at the load point.
3. Short circuit tolerance of the cable.
4. Mechanical strength of the cable.
A cable is selected fo the job that can meet all these
criteria.
Basically HT and LT cables are of same material but the
difference is in insulation.
Looks too much like a text book lesson. If you can post
your exact requirement, I would try to help.
Is This Answer Correct ? | 4 Yes | 2 No |
If I have Energy Meter Ratio as 100:5 & Also I have CT Ratio as 50:5 then what will be my multiplying Factor(M.F.)
how will reduce the voltage. if 12volt/250ma transformer toreduce 6 volt
Why ground terminal is used in pot meter 10k ohms
DG lube oil and waste oil how to dispose outside and there is any authorised vendors will be there for this.
Is there any difference of regulation of transformer, alternator , transmission line, if yes, what is it?
why fuse not recomended to neutral
how LT meggar works
How we calculate the spacing between the conductors in 11,33KV lines?
Why does an induction generator is preffered as compared to synchronous generator in especially a wind energy power production project?
which safety we have to take when we go for work?
How to calculate the voltage drop of 4 Core 50 Sqmm SWA cable for a distance of 350 mtrs and what can be the maximum load connected to it?
what is difference b/w squirrel cage rotor and wound rotor