How Calculat the Cable Sizing of HT/LT System & Explian by
one Exampal?
Answer Posted / habib
Cable size (sq.mm.) is selected dpendent on 4 facors
1. Current carrying capacity (popularly termed Amapcity)
of the cable.
2. Voltage drop that can be tolerated at the load point.
3. Short circuit tolerance of the cable.
4. Mechanical strength of the cable.
A cable is selected fo the job that can meet all these
criteria.
Basically HT and LT cables are of same material but the
difference is in insulation.
Looks too much like a text book lesson. If you can post
your exact requirement, I would try to help.
| Is This Answer Correct ? | 4 Yes | 2 No |
Post New Answer View All Answers
What is the basic principal, by which DC voltage level is increased more than the supplied AC voltage during conversion. As upto AC level it is contorrled by firing anlge but after maximum level how is it possible.Please clear picture. OR we have to supply the higher level AC?
IF I KNOW THE AREA OF CROSS SECTION OFTHE WIRE , WATTAGE OF THE LOAD ,VOLTAGE SUPPLY WHAT IM GIVING TO THE LOAD AND ALSO POWER FACTOR OF LOAD ....... SO GIVE ME FOR WHAT AMOUNT OF CURRENT I SHOULD USE WHICH TYPE OF CABLE?
where are the circulat the diesel in DG parts name with pictue
What is the difference between Generator Differential Relay and Transformer Differential Relay?
is there any device that works properly accept relay, it may be fuse but if i want fuse of 33kv 300 amp it is avaliable, pls give me details
If we use 250A MCCB as a incomer in Control panel for a fault level of 50kA for one second ,assuming temperature rise from 85 Deg. to 100 Deg , Then what will be the Aluminium Bus-bar size for 250A MCCB? Explain in detail.
If we have 11 kv RYB Phase single core cable near about. Then wht effect and losses
Is there chopping current in resistive circuit
write a program that prints prime numbers from 1-20 in digonal form
What is signal flow graph?
from generating station If 400v LT line length is 1000m how much voltage is drop and how do i calculate it? which cable will be use for this line?
How delta connection in the primary of distribution transformer reduces harmonics?how delta connections reduces harmonics?Please answer me...Hope that question is correct.
What are the advantages of instrument transformer?
Mention what are the types of semi-conductors?
Connection diagram for KW meter and Kva meter