Answer / mm
the anti pumping device is used to avoid continously
energising the breaker closing coil once the CB has already
closed. this is done to avoid burning the coil
Is This Answer Correct ? | 85 Yes | 12 No |
Answer / s.prakash
The anti-pumping relay allows the breaker to close only
once for each press of the 'close' pushbutton (or rotation
of the handle).
Is This Answer Correct ? | 58 Yes | 11 No |
Answer / k.ramesh,vepl
This Coil is used to avoid the continuous supply of the
breaker coil during faulty condition,once we are giving the
closing pulse during uncleared faults condition the breaker
will close one time only. After we are giving many more
closing pulse to the breaker,cannot perform that closing
operation with the help of anti pumping coil.
Is This Answer Correct ? | 48 Yes | 7 No |
Anti pumping relay is used to prevent closing coil from
being burnt by the repeated closing command. Closing coil
is not designed for continuous electrical operation and
once the closing coil is energised, breaker will get on and
it will be remain energised mechanically until any trip
command is available. So continuous supply is not required
for closing coil.
Is This Answer Correct ? | 33 Yes | 8 No |
Answer / sukhdev negi
the anti pumping device is used to avoid continously
energising the breaker closing coil once the CB has already
closed. this is done to avoid burning the coil
Is This Answer Correct ? | 20 Yes | 5 No |
Answer / ahmed arafa _bapetco
Anti-pumping relay is used to avoid closing of the circuit
breaker when there is afaulty case , so the closing coil of
the circuit breaker can not be energised until the path is
healthy and the trip is not exist
Is This Answer Correct ? | 15 Yes | 4 No |
Answer / lokesh thota
Pumping means if breaker is close & give close command (electrical or manual) to it,spring will discharge & charge again. To prevent this pumping anti pumping feature is required,which in turn will help to restrict unnecessary operations of breaker mechanisms.
Is This Answer Correct ? | 9 Yes | 9 No |
The function of Anti Pumping relay is to cut off the supply to CB closing coil in case of TNC switch spring failure and prevent CB hunting effect i.e. continuous closing, opening operation.
Is This Answer Correct ? | 0 Yes | 0 No |
A device, which function to trip a circuit breaker, contactor or equipment or to permit immediate trip by other device or to prevent immediate re-closure of a circuit interrupter in case it should open automatically even through its closing circuit is maintained in closed condition.
Is This Answer Correct ? | 1 Yes | 2 No |
why Transformer and DG rating capacity is in KVA
What is ignitor and why it is use in Hpmv lamp ?
The maximum demand of consumer is 2 kW and his daily energy consumption is 20 units. Its Load Factor is (1) 10.15% (2) 41.6 % (3) 50 % (4) 60%
3 phase supply is there Total kw 100 howmuch cable put the load
The advantage of free wheeling diode in a Full Ware rectifier is -reduces the harmonics -Supplies the voltage at negative vlotage
why h parameter are called as hybrid parameter?
For a spring controlled governer the relation F = ar+b (F is the controlling force, r is the radius of rotation a and b are constants), indicates that the governer is
what is meant by dedicated earthing?
what is the effect of power factor to (a) voltage (b) transformers (c) generators (d)transmission lines
how i prepare for the written test in mahagenco?
2 Answers MahaDiscom, MahaGenco, Wipro,
Minimum IR value of 1.1 kv grade 3.5c (300, 240,185,150,120,95,70,50,35,25) sqmm Aluminium XLPE cable and 4c (16, 10,6 & 4) sqmm cu arm cable between RY,YB,BR,RN,YN,BN,RE,YE,BE & NE.
why transmition and distribution and genaration of voltage in multible of 11 means 220v,440v,11kv,22kv,,,...so on