what is the use of Antipumping in HT breakers.
Answers were Sorted based on User's Feedback
Answer / mm
the anti pumping device is used to avoid continously
energising the breaker closing coil once the CB has already
closed. this is done to avoid burning the coil
| Is This Answer Correct ? | 85 Yes | 12 No |
Answer / s.prakash
The anti-pumping relay allows the breaker to close only
once for each press of the 'close' pushbutton (or rotation
of the handle).
| Is This Answer Correct ? | 58 Yes | 11 No |
Answer / k.ramesh,vepl
This Coil is used to avoid the continuous supply of the
breaker coil during faulty condition,once we are giving the
closing pulse during uncleared faults condition the breaker
will close one time only. After we are giving many more
closing pulse to the breaker,cannot perform that closing
operation with the help of anti pumping coil.
| Is This Answer Correct ? | 48 Yes | 7 No |
Anti pumping relay is used to prevent closing coil from
being burnt by the repeated closing command. Closing coil
is not designed for continuous electrical operation and
once the closing coil is energised, breaker will get on and
it will be remain energised mechanically until any trip
command is available. So continuous supply is not required
for closing coil.
| Is This Answer Correct ? | 33 Yes | 8 No |
Answer / sukhdev negi
the anti pumping device is used to avoid continously
energising the breaker closing coil once the CB has already
closed. this is done to avoid burning the coil
| Is This Answer Correct ? | 20 Yes | 5 No |
Answer / ahmed arafa _bapetco
Anti-pumping relay is used to avoid closing of the circuit
breaker when there is afaulty case , so the closing coil of
the circuit breaker can not be energised until the path is
healthy and the trip is not exist
| Is This Answer Correct ? | 15 Yes | 4 No |
Answer / lokesh thota
Pumping means if breaker is close & give close command (electrical or manual) to it,spring will discharge & charge again. To prevent this pumping anti pumping feature is required,which in turn will help to restrict unnecessary operations of breaker mechanisms.
| Is This Answer Correct ? | 9 Yes | 9 No |
The function of Anti Pumping relay is to cut off the supply to CB closing coil in case of TNC switch spring failure and prevent CB hunting effect i.e. continuous closing, opening operation.
| Is This Answer Correct ? | 0 Yes | 0 No |
A device, which function to trip a circuit breaker, contactor or equipment or to permit immediate trip by other device or to prevent immediate re-closure of a circuit interrupter in case it should open automatically even through its closing circuit is maintained in closed condition.
| Is This Answer Correct ? | 1 Yes | 2 No |
R u say ,that is there is any flux in your room.
Why HT voltages are expressed in 11KV,22KV,33KV and so on? (ie in times of 11)
How to determine the breaking capacity such as break down current and break down voltage for VCB and CT's.
how many types of ratings are there of transformer
Where can I get Iidian straderd specifications for electrical items or works in web? please help me.
will three phase energy meter run without one phase
what is the advantage of Cathodic eathing system and what is the basic principle and how itis working, please explain clearly .
how to find diesel consumption of 600kva DG per hours????
How to calculate earth wire load by formula
anybody can give the voltage value for 1M ohm
In short transmission line,why does the receiving end voltage is less than sending end voltage?
What current can be carried by 25 sqmm copper cable safely?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)