OUR METER READER TAKE READING OF INDUSTRIAL CONSUMER.THEY
ALWAYS ASK HOW TO INCREASE POWER FACTOR FROM 60% TO 99 % TO
AVOID PENALTY OF POWER FACTOR.
Answers were Sorted based on User's Feedback
Answer / zahid noor
Power Factor can be improved by installing Capacitors at
the end of consumer, why it is required, in order to
fulfill the loss during transmission of power to the end
of consumer, henceforth if consumer installs additional
capacitors for making this loss, penalty for PF below .95
can be avoided & for PF above .95 to unity , extra rebate
on monthly bills can be availed. Henceforth It is always
beneficial to achieve PF up to Unity.
In order to calculate the KVAR of capacitors to be
installed, it is required to know the details of consumer
regarding load, voltage level, type of load, switching
operations of load so as to finalize the capacity required
for achieving the same.
| Is This Answer Correct ? | 5 Yes | 1 No |
The power factor is low for industrial customer because the load is usually inductive due to the many motors installed.
Power supply companies sell by calculating KWH used.Thier generators maximum capacity is limited by the amps the generator can produce at a fixed voltage.
So calculations will tell u that lower power factor means higher amps for the same KWH &AND HIGHER PF MEANS LOWER AMPS for the same kwh. thus the power supply companies can make more money from the same generator and also save on other expenses.
power factor is improved by connecting reactive load in parallel.this reactive power is loss free and you dont pay for the power consumption.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / t.mohan
POWER FACTOR = REAL POWER / REACTIVE POWER.KWH/KVRH.
FOR INCREASING POWER FACTOR PROVIDE CAPACITOR BANK AT
CONSUMER'S END.
| Is This Answer Correct ? | 1 Yes | 0 No |
If one lamp connect between two phases it will glow or not?
Explain working of PIU(Power Interface Unit) in Telecommunication,
7 Answers ACME, ATC, Bharti, HCL, INDUS, Pace Pharmaceuticals,
what is control supply rating of a machine
How to select the Cable size for 550 Amps Load without seeing the cable Catalogue?
HOW DO I CALCULATE OVER LOAD RELAY & CONTACTOR IN DOL STARTER? & in dol why it is require circuit breaker?
how to calculate current carring capacity of cable and cable selection? 1) copper flexible cable 2) copper armoured cable 3) Aluminium cable
How to test the vector group of a Yd11 transformer? what are the relations to be checked between various vectors to confirm this vector group?
name the famous power plants present in A.P
For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply was applied at the HV. Connection between Aa was made with a 2.5mm cable. As soon as power was switched on the cable caught fire and burnt. This test was then abandoned. It is noteworthy to say that a similar cable was also used in a similar transformer for the same. The cable did not burn and test was successfully completed with good result. What is wrong? Please, help me out.
will the turbogenerator operate on leading power factor with out modification in the stator winding.
if flow of electrons is current then why their direction are different???
3,12,24,33,_ ,75,150 Find the missed number in this sequence
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)