Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to select DG set for certain load?

Answers were Sorted based on User's Feedback



how to select DG set for certain load?..

Answer / soumendasbiswas

Depending upon the total load and maximum demand of that
plant...

Is This Answer Correct ?    21 Yes 7 No

how to select DG set for certain load?..

Answer / rajani

Actually DG size has to select depends on maximum demand
and considering base load and starting load and step load

base load = total maximum demand - loads which are
taking high loads at startign

starting load = if motor loads are DOL starts 6 times to
the Ifl will take at starting and soft
starters /VFD's will take 3 times to Ifl
step load = Whwn the main power supply is off
immidiently what are the load we can
switched ON through DG -called step load
(generally 40-60% of Dg load can be ON as
first step)

So our selected DG shopuld meet the step load and capable
to withstand startign loads

Is This Answer Correct ?    12 Yes 5 No

how to select DG set for certain load?..

Answer / sheo

Suppose LOAD-1000 KW

So design load of Genset @ 80% inefficiency.
and power factor @80% in case of ( Failure of capacitor)because life of Capacitor and Gen set never equal to each other.
so 100% power back-up for 1000 KW load required DG 1000/0.64=1562.5 KVA

Recommended DG-1500 KVA

Is This Answer Correct ?    5 Yes 0 No

how to select DG set for certain load?..

Answer / rakesh kumar sharma

generally the efficiency of the D.G.set is 80% because of
the power factor.so u have to add 20% on the entire
load.

Is This Answer Correct ?    6 Yes 3 No

how to select DG set for certain load?..

Answer / sijish

DG normaly loads up to 80% of the full load rating,

First step.Calaculate the load in KW.
Consider the staring current of the Load.
The minimum Amps rating of the dg shoul be 4 Times the
Running current of the motor load

Is This Answer Correct ?    2 Yes 0 No

how to select DG set for certain load?..

Answer / anil

Depending up on the total load to select the dg.for 5kw
load 10kva DG is suitable.
dg can be loaded for 80% of full load ,ie 8kw
calculating PF 6.4 kw can be loaded in 10kva dg.

Is This Answer Correct ?    2 Yes 1 No

how to select DG set for certain load?..

Answer / m.prabhakar

Depending up on the total load to select the dg.For example
180KW load is there 200kva capacity genarator is sufficient.

Is This Answer Correct ?    23 Yes 29 No

Post New Answer

More Electrical Engineering Interview Questions

How to calculate no of EARTH PIT? Describe the formula as per IS standard?

0 Answers  


As we know,charged clouds(from which lightning stroke initiates)may be charged with either +ve charge or -ve charge. Now say one cluster of cloude is fully charged with +ve charge & another cluster is fully charged with -ve charge. In the sky these two cluster of charged clouds have come in such a distance that, if they come clouser by some few yeards then the lightning discharge will take place between these two cluster of clouds. Under such a situation an Aircraft came inbetween. what happend??

5 Answers  


how can calculated the rating of the 11 KV transformer?

6 Answers   NBCC,


What is the difference between ground & earth or neutral

1 Answers  


how to deside the capacity of chock for drive?

0 Answers   Essar,


what is differentila pilot supervision in the incomer control panel in the power station?

0 Answers  


1.What is the range of stator resistance of 3-phase induction motor? 2.Two electrically operated vibro motors are foxed in parallel direction in vibrating feeders. what is the direction of both vibro motors?

0 Answers  


what is the reactive power what is the use of it in system

0 Answers   L&T,


why fuse is not applicable for nutral and what will happen when it applied.

4 Answers  


what is a speed of rotor when we give supply to stator of 50hz and as well as rotor of 60hz of an induction motor?????

0 Answers  


what is anti-pumping relay and the significance of it in a switcgear cb control system?

1 Answers  


How LT megger works ?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)