Why not implimenting power factor in Diesel generator
Answers were Sorted based on User's Feedback
Answer / ravi
In case we correct the existing P.F. in case of DG set by
putting capacitor panel across DG set, then there is no
harm until the cicuit draws inductive or lagging P.F. . But
in case it starts drawing leading P.F. due to addition of
excessive capacitors across D.G. set then the output
terminal voltage would be higher than the induced voltage.
so it is not desirable to operate cap. panel across DG set.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / rvg.msceb
Offcourse, p.f is the property of load. In a DG set, prime
mover supply mechanical BHP to the alternator, and it does
not depends on the load characterestics, but depends on the
load current.
in short, an alternator demands higher input torque/power
from the prime mover, as soon as current increases from
alternator.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / bijaya
Yes, we can put capacitors across DG load but it should have a controller ie capacitors should switch on automatically to maintain PF around 0.96 and manual operation of capacitors are not advisable .
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.p.sharma
We maintain the P.F. of DG Set approx 0.95 by two methods :-
1.By decreasing the voltage
2.By using power capacitor
Advantage is that for higher PF load current will be low to
deliver the same KW/MW from DG Set.
| Is This Answer Correct ? | 4 Yes | 4 No |
Power Factor is the property of load. Generator is a source
of power. So it can not be corrected thru generator. However
Synchronous generators can regulate power factor by
adjusting it's excitation current.
| Is This Answer Correct ? | 4 Yes | 6 No |
Answer / vishal
in diesel gen. you adjest p.f. with exitation inc/dicrese
easy.
| Is This Answer Correct ? | 0 Yes | 2 No |
what is the UPS
why we use iron corn in transformer instead of wooden core
why the all high voltage transformers are in 11kv , 33kv , 66kv, 132kv like that
Bimetal strip used in overload relay what is that,which types of material used for that & percentage.
IF TVM OF TRANSFORMER SHOWS POWER FACTOR ON 33 KV SIDE AS 0.97 LAGGING AND ON 132 KV SIDE IS 0.75 LEADING.IS THIS CORRECT.WHERE IS PROBLEM.
Whether amorphous core transformer is commercialized or not:Name of company making amorphous core transformer and what are different rating?
why voltages are multiple of 11 or 1.1???describe with derivation plzzz.thanks
What is the current flow in 230v ac supply ? What is the current flow in 415v Ac supply ?
how i can calculate the size for fire cable
How is the percentage impedence of a transformer fixed at design stage???
sir please send me iocl written test paper in my e-mail account. i'll be obliged to you........ thank u roshan
If DC supply is given to a transformer it may a) Work b)Not Work c)Give lower voltage than the rated voltage on secondary side. d)burn the winding
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)