what is RMU ?
Answers were Sorted based on User's Feedback
RMU stands for Ring Main Unit having at least three
switches ( Breaker or isolator os load break switch)
connected with a bus with mechanical interlocking as per
system requirement.It can used upto 11KV with bus loading
capacity 630 A . Breaker may be of rating 200A or 630A as
per requirement. Two LBS can be used as two I/C and CB as
out going feeder or DT feeder as per requirement. In this
way O/G or DT feeder can be feed through second I/C if
supply from first I/C intruppted due to any reason. So RMU
reduce the supply ontrupption time.Many RMU's can be
connected in a ring mode in a distribution system.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / dhana sekhar
Distribution networks are normally formed by interconnecting
a number of ring shaped grids. Distribution transformers are
then connected to the system by T-offs. Instead of
specifying and selecting individual components required for
a T-off, the required components are frequently available in
an integrated package known as a ring-main unit (RMU).
| Is This Answer Correct ? | 6 Yes | 1 No |
Ring Main unit, its used at main input to the industries. having the voltage input of 11000 volts. its having two feeders from same sub stations. incase of one feeder fails we may turn on another feeder. high profiles industries & offices using SF6 type of RMUs.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pravesh mishra
rmu is ring main unit ,it is used in 11 kv under ground.the two 630 ampr.load break isolator the rmu shall be connected to the incoming and out going ends of the 11 kv ring system for the control of the 11kv ring distribution systenm .the 630amp.sf6 breaker of the rmu shall be connected to control ,protect and isolator the 11kv/433v didtribution x-former / ht consumers/connected through 11kv bunderground cable
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / a jalil
Ring Main Unit. RMU used for H.T.side. RMU is having
3no.s of switches(Circuit Breakers or Isolators or LBS), it
is used for two inputs with mechanical or electrical
interlock and one outgoing to the load. Either one input
with two outgoings. RMU used for redundancy feeder’s
purpose.
| Is This Answer Correct ? | 1 Yes | 0 No |
RMU as an important part of secondary distribution substations. Ring main unit is a totallty sealed, gas-insulated compact switchgear unit.
| Is This Answer Correct ? | 1 Yes | 0 No |
RING MAIN UNIT IS 2 TYPE NUMBER(1)RMU (MINERAL) OIL TYPE NUMBER(2)RMU SF6 GAS TYPE (SULFUR HEXAFLUORIDE)
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vijay
rmu means ring main unit,it used for ht cables only it act as like isolator .
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rahul mistry
ring main unit is used for power distribution and also use
for transformer procation in rmu there are three or fore
function inside one fn is incoming supply and other three Fn
for supply distribution
| Is This Answer Correct ? | 0 Yes | 0 No |
Between educational qualification and practical work experience, give us a brief explanation on your practical experience in your past Endeavour that you performed well to the satisfaction of your past or present employer?
To generate electricity , what is the speed of rotor?
What should be the percentage increase in length of the dead end clamp for bus bar conductor (Hawthorn) after hydraulic pressing and what should be the applied pressure?
What is servo Motor? What's the advantages of this motor over Induction motor?
how we can measure the dc current instead of clamp meter ?
lightning arrester rating selection procedure: (line to line voltage(kV)/(squ.root of 3))*squ.root of 2. now the question is, IS this above formula correct for both STAR and DELTA connected system???
which Machine u will prefer to use at place where Flammable gases are coming out & why ??
How to calculate impedance volt in Transformer?
What are applications of Shunt release?
2 Answers Techno Electric and Engineering,
why Transformers power mentioned in KVA?. and why Generators and Motors power mentioned in KW?.
the grid connection required for a 50 MegaWatt fotovoltaic powerplant is higher or lower than 35kv (high or medium tension)?
what is the defination of Cable database? What are the points are considered while preparing cable database? Is there any sample available for cable database?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)