why neutral of 6.6 kv star connected sq. cage induction
motor does not get earthed, though for earth fault
protection it is must.
Answers were Sorted based on User's Feedback
Answer / siddharth tayade
there is no need of star point for earth fault detection we
can connect the c.t. as per the earth fault requirement
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / budhaa lal
because we use the CBCT both side(feeder side and in motor
winding R,Y,B.)and for earth fault protection we give the
both ct's output to the motor protectio relay. and when
earthfault ocurres in motor there is unbalance in core
respectively and sensing by motpro relay and it gives
tripping as per setting.
| Is This Answer Correct ? | 2 Yes | 4 No |
Hi Pratikjain,
The answer in #4 is partly correct. Your question is on the
motor and not on the feeder. Provide appropriate cts and
wire correctly using an over-current earth fault relay.
Note, this relay has three operating elements known as red,
yellow and blue-phase elements. The yellow-phase element is
for earth fault. This relay works on the principle that Ir
+ Iy + Ib = 0 for a balanced load. This summation is
algebraic. In times of an earth fault the above equation is
no longer equal to zero hence the residual current flows
through the yellow-phase element as an earth fault provided
your cts and relay are properly connected. In this way the
cb for the motor is tripped by the yellow-phase element as
an earth fault if the relay is properly set.
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / venkatesh
the fundamental condition for connecting neutral to earth is that the neutral voltage should not be higher than supply potential .but in star connected squirrel cage induction motor the neutral potential was reached uplimit potential during starting.so, neutral was not connected to earth in that case while in transformers there is no problems of increased neutral potentials. though they were similar in some aspects
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / velusamy
THE PURPOSE OF PROVIDING STAR CONNECTION IS 1.DEPENDING ON
THE DESIGN REQUIREMENT OF EQUIPMENT 2.TO PROVIDE PROTECTION
AGAINST DIFFERENTIAL
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / rajesh
As the neutral has high potential when the motor starts.
And else decreases while running. This may cause high flow
of current to earth which is earth fault.
| Is This Answer Correct ? | 0 Yes | 9 No |
Answer / nanoty
Because it is a high voltage rating motor and Star
connected.There is no need of earth fault protection in
this case.
| Is This Answer Correct ? | 0 Yes | 14 No |
hi friends how 3 phase converter functioning ?what is working principle of rotory phase converter ?
A distribution transformer giving afrequency of 200HZ, where it is rated for 50HZ. when it will occure?
In supply RYB are mentioned. But in transformers, why they are mentioning XYZ?
What is the name of oil which is used in transformer?
Can 2 nos. of 1 ton split ac be used through a 20 am supply meter?
why secondary of c.t. will kept open ?
Why the motor was take the starting current is high?
why the amount of voltage generated at power generating stations is 11 KV only....?
Please tell me the formulaes while designing a substation for power Calculations in designing a 33 KV Substation?????
what is battery impedance testing and how we perform this test with four wires.
What is the correct procedure to shutdown VCB in 11kv substation.safety and work procedure
What is meant by coupling capacitor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)