In what circumstanced the CT used for protection relay will
be saturated?and what will happen to the relay is the CT is
saturated?
Answers were Sorted based on User's Feedback
Answer / nilamani
if we will operate the CT in open circuit then due to heavy
magnetising current due to primary winding will effect the
saturation ll be affected.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / tameshwar singh
The CT saturation occurs when secondary winding is kept
open. At this time there is no demegnatising current flows
in secondary winding and due to this primary winding will
carry very high megnatising current.As the high megnatising
current produces high megnatic flux which causes the CT
core saturation
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / santhosheee
Normally Protection CT will designed by some saturation
level ie Knee Point Voltage. its depepending upon the
protection level. for example if any fault the voltage will
build up in the CT because its transfomer.according to
fault level the manufacturer designing the CT with some
saturation level. If any heavy fault Like lightning,( some
time substation system will affect heavy lightning ) may
be that time and above knee point voltage the CT will be
saturate. its like a short circuit in the CT winding. so
flash over may occur in the CT.
| Is This Answer Correct ? | 5 Yes | 5 No |
plz explain TSM and PSM.with example suppose ct ratio is 4000/5 and tsm is .15 and plug is at 3.75 if fault current is 8000A.so how i find relay oprating time.
2 Answers College School Exams Tests, ME,
what is the definition of Nominal current or voltage
I am having a 1500 KVA transformer whose secondary current is 2086A and my connected load is 1000 KVA, I am having 400 KVAR APFCR for PF improvement what ratio of CT should i install in LT EB Bus to get optimum PF improvement?
In a 3 phase system a neutral exists so that any unbalanced currents can flow through it towards earth.... but a phase demands a particular current as per the load attached to it....then where does the extra current come from the goes in the neutral??....I mean in an unbalanced system a phase demands a current as per its load attached....then where does the unbalanced current come from??
WHAT HAPPENS IF FUSE IS CONNECTED TO NEUTRAL WIRE
Is there any calculation to find unknwon(unferroled) phases R Y B in alternator,3 phase motor anybody shoot my problem. how can we notice this is the respective phase?
There is any especial requirement for motor to drive through with VFD?
suppose i have two single and three phase induction motor,thier have not any rating on its panel,anybody can tell me which motor is single or three phase?
how we masure a cuurrent?
prove that power consumed in 3 phase delta system is 3 times as compared to 3 phase star system
what is the difference between high impedance REF & REF, same high impedance differential protection & differential protection for Power transformer?
calotropis is an example of the following phyllotaxy
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)