How does frequency affect KVA rating of a transformer?
If a 500 kva, 500 to 250 v, 60 hz t/f normally used in Canada is to be operated in Europe on 50 hz
frequency then how will its KVA rating change?
a-increase
b-decrease
c-remains same



How does frequency affect KVA rating of a transformer? If a 500 kva, 500 to 250 v, 60 hz t/f normal..

Answer / jinboll

The transformer EMF equation shows that the EMF induced in the secondary or the primary side of a transformer is directly proportional to the product of the flux (Φm) through the transformer core and the frequency. This leads to the flux is proportional to E/f.
For example, the kVA rating of the 500v to 250v 60 Hz transformer will be smaller when used in Europe with a frequency of 50Hz.
500/60 = E/50 E is smaller than 500v on primary side.
250/60 = E/50, E is smaller than 250v on secondary side.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Is there any scope for an electrical engineer in MRF company......

1 Answers  


what is a difference berween line voltage and phase voltage?

2 Answers  


what purpose to use excaiter in DG.?

0 Answers   TATA,


how to know the diffrential relay setting of 06mva step- down (delta-star)transformer?

0 Answers   IPCL,


what type of euse we should use ? 1- High resistance & low temperature 2- High temperature low resistance

2 Answers  






how many types of transformer.

3 Answers   Technocrats,


While testing a ZCT what parameters have to check or measure?

0 Answers   Indian Railways,


how ups works ? various parts of ups and working principle

0 Answers   Serco,


In Induction machines which type of emf is induced ( statically or dynamically)?

1 Answers  


how to protect motor in dol starter having capacity of 30 hp.40 hp?

0 Answers  


why generator and t/f ratings given in kva?

2 Answers  


WHAT SHOULD BE THE BEST CURRENT RATINGS (PRIMARY / SECONDARY)FOR A CT INSTALLED AT THE INCOMING 11KV PANE? WILL IT BE CALCULATED ON THE BASES OF MAXIMUM DEMANT VALUE OR ON SUM OF ALL TRANSFORMER'S KVA? NOMALLY MAX DEMAND REPRESENT THE MAXIMUM OPERATING LOAD OF THE PLANT AND TOTAL KVA OF (SAY 5 NUMBERS TRANSFORMERS) REPRESENT THE CONNECTED LOAD. WHICH i.e. MAX DEMAND KVA OR CONNECTED KVA ARE BETTER TO USE FOR CT CURRENT CALCULATION? PLEASE ANSWER.

0 Answers  






Categories
  • Civil Engineering Interview Questions Civil Engineering (5073)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4444)
  • Electrical Engineering Interview Questions Electrical Engineering (16591)
  • Electronics Communications Interview Questions Electronics Communications (3915)
  • Chemical Engineering Interview Questions Chemical Engineering (1092)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (214)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (258)
  • Instrumentation Interview Questions Instrumentation (2986)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (122)
  • Power Plant Engineering Interview Questions Power Plant Engineering (170)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (0)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1377)